I am planning to run 6mm SWA from a main DB which is protected by a 40A fused switch. The SWA runs to a garage and is connected to a BS1361 40A, it then goes into an RCBO protected sub main board. Is the BS161 necessary at the sub main when there is 40A protection at the source?

Any advice would be greatly appreciated.
 
. .
 

Attachments

  • [ElectriciansForums.net] Garage Sub Main BS1361
    indexmmmm.jpg
    6.7 KB · Views: 114
Defo ditch the 1361 and what are you connecting in the garage - if you have a socket circuit then an RCBO is a must, if you have a lighting circuit and its all surface, just fit a MCB.
 
A DIYr (previous owner) made it all a bit complicated not least, not connecting any external earths to the main ET of each board! All sorted with 3 new metal sub mains all containing RCBOs. I am just about to be assessed by NICEIC and wondered about BS1361's. The sub main supply goes from house and splits underground - one sub going to garage and the other to workshop. The BS1361 above is in the workshop which I will remove and I suppose that I should do the same with the garage BS1361 (it might even be 60A) not sure what would happen if I left it in? I am on a steep learning curve but glad to learn all I can.

Thanks for your comments.
 
Thank you for your comment. The SWA in the garage is is surface mounted and the supply partly buried. I am newly qualified and mad keen at the moment hence wanting to do it right. The fog is getting a little thinner! Thanks guys for all your help.
 
well i wouldn`t mind knowing what the earthing arrangements were here first Murd...

Yep, what earthing system, and is there any extraneous metalwork/pipes in the workshop or garage that need main bonding to the sub-boards EMT??

Kind of wondering about this SWA cables underground split and if the continuity of the SWA is being maintained throughout?? Have you made any checking tests at all for this SWA cable??
 

Reply to Garage Sub Main BS1361 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top