Hi Guys

Just seeing what you all use use for buried garden light connections, to seal up fully from the elements/ vermin?

Been using 3M gel connectors for a while without any issues.
https://multimedia.3m.com/mws/media/1983303O/3m-scotchlok-idc-connector-314-datasheet-en-eu.pdf?&fn=EMD_EMEA_Scotchlok-IDC-Connector-314_TDS_AABBDD51044_EN03_R2.pdf

Just been back to check on a job (tripping out) and looks like the gel has been eaten from inside the connectors.
Quite a few dead suspect ants 🐜 had found there way into our galvanised box !!

Have seen the wiska pourable gel, anyone use this ?

Thanks Sy

IMG_5268.JPG


IMG_5267.JPG
 
First problem: That box is not suitable for outside use. It isnt sealed in any respect. The fixing holes at the back will let in water and (as I can see) the top knock out has pushed in allowing more wet + critters to nestle in there.

There are proper junction boxed for burying. eg PRATLEY
You could try a WISKA box plus their MAGIC GEL
 
First problem: That box is not suitable for outside use. It isnt sealed in any respect. The fixing holes at the back will let in water and (as I can see) the top knock out has pushed in allowing more wet + critters to nestle in there.

There are proper junction boxed for burying. eg PRATLEY
You could try a WISKA box plus their MAGIC GEL
Thanks for the reply (and b@llocking 🙈).... so the Wiska Magic Gel is good then.

Time to give it a try I think
 
For buried connections for garden lighting etc, I use wiska boxes, wago 221's, and gel (I use the raytech magic gel, but I expect the wiska stuff is much the same). IMO gel is the only reliable way to do these junctions underground. CW glands for armoured cable, compression glands for flex.

I've also seen it done with galv. besa boxes, which actually hadn't corroded as much as you'd expect, as had been there a while (old colours).
 
If it's underground I've always favoured SWA with good old fashioned resin joints. I would make a 3 way resin joint below ground, no enclosure necessary and would have used a short section of HO7 cable through a diagonal drilled hole into the bollard. It's swings and roundabouts, if there's a future fault it makes life awkward but the chances of a fault ever occurring are pretty slim.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

sythai

Arms
-
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Garden lights... IP68 + vermin protection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
sythai,
Last reply from
Marvo,
Replies
4
Views
559

Advert

Back
Top