Hi, I was wondering if any of you have ever used Garo RCBO's. They do a single module dp RCBO which would be handy for TT systems.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Garo in the UK Electrical Forum area at ElectriciansForums.net
They appear to be partnered with Socomec, I've used Socomec for a lot of LV control gear.
Good quality, a lot of their items appear to been clones of eaton moller.
I can't guarantee their quality, maybe buy for one job and see how you get on? Do they provide CU's designed for a fully populated board of DP RCBO's?
They do boards to accommodate them. I was hoping to get one fitted into a MEM board. The problem I'm having is an intermitting fault on a lighting circuit. This then causes the main 30mA RCBO to trip which takes out a lot of the premises. So I was thinking of changing all the mcb's to double pole rcbo's and changing the main 30ma rcbo to a time delayed one so if there is a fault only the circuit with the fault will disconnect. What do you think?
Yes I see what you mean. If I used 30mA rcbo's single pole and changed the main 30mA rcbo to a time delayed one, would the single pole operate on a N-E fault before the time delayed one?
Hi, I was wondering if any of you have ever used Garo RCBO's. They do a single module dp RCBO which would be handy for TT systems.
Ive looked in to this before, Garo RCBO's are not single module double pole they are single pole switched neutral.
single pole switched neutral RCBO's will be fine for TT systems.If you had an upfront 100ma S type RCD and a neutral/earth fault developed on one of the circuits having a SPSN RCBO will isolate the neutral on that circuit.