Hi, I was wondering if any of you have ever used Garo RCBO's. They do a single module dp RCBO which would be handy for TT systems.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Garo in the UK Electrical Forum area at ElectriciansForums.net
Just had a look at some Hager (The make I usually use) RCBOs that one site says are 'SPSN'. However, when I look at the datasheet, it says they are Single Pole Solid Neutral. This is highly confusing.
What you want will be listed by Hager as 1P+N.
Cheers mate. Any idea where one can find a CU/Busbar to fit these? I have a TT CU change potentially coming up, and would prefer to use RCBOs