Hi all, another bonding question I'm afraid!

The Gas meter is in a brick built attached cupboard by the properties front door. The gas pipe runs around the outside wall of the house (on the outside) and enters through the kitchen wall.
Is it acceptable to bond near the meter or should it be bonded where the pipe enters the building proper. Hope this makes sense!
 
Thanks for quick replies, practically its easier to bond by the meter, is there no issue being it hasn't actually entered the building
Within 600mm (ideally) .....which means within 600 mm of the consumers side of the meter....so in answer to your question....yes.....
 
Decide where on the pipework you are going to bond it........and be sure to get it bright with a bit of wire wool first wont you mate..........
 
Yes I am going to bond by the meter. Thanks
Do you know the max value of resistance you should be looking for on an R2?....if not then take a look in GN 3....see if you can find it...get them bonds tight n all wont you mate...as they can come slack (due to thermal effects) in time.......:hippy:
 
but it can also be within 600mm of where it enters the building, so either point would comply.
 
Is not a tee a soldered joint?

Yes, but it can also be a compression tee. ;)

(The gas regs do not allow the use of compression joints in inaccessible places - just like sparks shouldn't use junction boxes in inaccessible places - and personally, I try to avoid using compression joints on all gas work.)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol

Thread Information

Title
Gas Bonding
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
bodders22,
Last reply from
Geordie Spark,
Replies
13
Views
1,703

Advert

TrueNAS JBOD Storage Server

Back
Top