well theres 542.2.1 and 542.2.4......
542.2.1: earth electrodes.
suitable earth electrodes shall be used. the following types of earth electrode are recognised for the purposes of the regs.....
earth rods or pipes
earth tapes or wires
earth plates
underground structural metalwork embedded in foundations
welded metal reinforcement of concrete (exept prestressed concrete) embedded in the earth
lead sheaths and other metal coverings of cables, where not precluded by regulation 542.2.5
other suitable underground metalwork
542.2.4
a mettalic pipe for gases or flammable liquids shall not be used as an earth electrode. The mettalic pipe of a water supply company shall not be used as an earth electrode. Other mettalic water supply pipework shall not be used as anearth electrode unles precautions are taen against its removal and it has been concidered for such a use.
543.2.2
a protective conductor may consist of the following
a single core cable
a conductor in a cable
an insulated or bare conductor in a common enclosure with insulated live conductors
a fixed bare or insulated conductor
a metal covering, for example the sheath, screen or armouring of a cable
a metal conduit, mettalic cable management system or other enclosure or electrically continuous support system for conductors
an extranious-conductive part complying with regulation 543.2.6
543.2.6
exept as prohibited in regulation 543.2.1 an extranious conductive part may be used as a protective conductor if it satisfies all the following requirements
electrical continuity shall be assured , either by construction or by suitable connection, in such a way as to be protected against mechanical, chemical or electrochemical deterioration
the cross sectional area shall be at least equal to that resulting from the application of regulation 543.1.1
unless compensatory measures are provided, precautions shall be taken against its removal
it has been considered for such use and, if necessary, suitably adapted
I dont know if this will help...but its there anyway....