Hi all. Can anyone tell me if it is acceptable to bond the gas pipe outside of the house rather than just after it enters? The problem is I have to bond a gas pipe- it was noted on a recent pir that it wasn't done, problem is it enters the house through the roof space of a two storey house, miles away from the fuse board. Getting an earth cable up there may be tricky. Looking an easier way out.
 
sometimes you can only bond where you can get to, providing its as close as possible and a note made on certificate stating where it is and why then no major issue.
 
^^^^^^^^^^^^^^^^^^ that's the one Lenny, OK external if there is a gas meter enclosure, or you can adapt some kind of enclosure around the pipe and label it, but left open to the elements IMO would not be acceptable.
 
I have just been informed by my electrician that we have to bond our gas pipe. The problem is that the gas meter is within a housing on the front external wall of my house and apparently he has to connect this back to my fuse box etc which at the farthest point on the rear of the house. Running this through the house is not an option, and the only opther idea he has is to run a conduit right around the perimeter of the property which will be an eyesore! Are there any other options? Can it just be earthed straight to the ground or is this something different?
 
I have just been informed by my electrician that we have to bond our gas pipe. The problem is that the gas meter is within a housing on the front external wall of my house and apparently he has to connect this back to my fuse box etc which at the farthest point on the rear of the house. Running this through the house is not an option, and the only opther idea he has is to run a conduit right around the perimeter of the property which will be an eyesore! Are there any other options? Can it just be earthed straight to the ground or is this something different?

The method your electrician has suggested is quite a common one, if you cant get to it through the house.
 
and until carlsberg make wireless bonding , you're stuck with it. the only other option would be to bond nearer to the CU, but that would contravene the " within 600mm of the point of entry" .
 
I have just been informed by my electrician that we have to bond our gas pipe. The problem is that the gas meter is within a housing on the front external wall of my house and apparently he has to connect this back to my fuse box etc which at the farthest point on the rear of the house. Running this through the house is not an option, and the only opther idea he has is to run a conduit right around the perimeter of the property which will be an eyesore! Are there any other options? Can it just be earthed straight to the ground or is this something different?


FROM CHRIS MURPHY - I HAVE ALSO POSTED THIS REPLY ON ANOTHER THREAD ABOUT EARTHING A GAS PIPE - ALSO IN ANSWER TO dboi75 - THIS IS WHY THERE IS A REFERENCE TO WHETHER THE GAS SUPPLY TO THE METER WOULD BE OF MILD STEEL PIPEWORK:


"Hello dboi75",

The Electrical Professionals on here WILL advise You correctly regarding Earthing the Gas Pipe to your Property - BUT - First a comment regarding whether the Gas Supply Pipe to the Meter is `Coming into Contact with Earth`:

Depending on the `Age` of this Gas Supply Pipe to the Meter it may NOT be a Mild Steel Pipe - The Practice of siting the Gas Meter outside a Property is a fairly recent one [Last 20 Years approx. in most cases] - This time scale would fall within the period where `Plastic` Gas Supply Pipework has been used - with Electrofusion Jointing.

So it does NOT necessarily follow that the Supply Pipe to your Meter is Mild Steel - Even if it was the Earthing of the Gas Supply Pipework FROM the Gas Meter TO your Property has to be carried out in the `Correct Manner`.

However - I did raise a point on here recently about WHY Electricians who I had used to Earth the Gas Pipework that I Install did NOT usually want to run the Earth Cable TO the Meter Box / Within 600mm of the Meter Outlet - and there were some comments about the Earth Connection being applied - `As the Pipe Enters the Building` - IF You can get confirmation of this as being an `Acceptable`/ `Within the Regulations` Method of connecting the Earth Cable to the Gas Pipework it would obviously be YOUR `Best Way` of adhering to the Electrical Safety Regulations.

Your Electrician obviously DOES NOT Feel that He can Adhere to the Regulations by doing this - OR He would have mentioned doing it this way ?


I thought that I should mention this to you - Just in case that it CAN be done this way [?]

I expect that there WILL be Conflicting Opinions about this `Method` of Earth Connection !


Chris - Registered Gas Installer / Heating Engineer.
 
Last edited:
earth bonding?....gas and water pipes are extranious conductive parts......that is to say that they do not form part of the electrical system within your home and as such are "bonded".....exposed conductive parts are conductive parts that form part of the electrical system and as such are "earthed"......
 
Isn't there a reg somewhere that if copper water pipes can be confirmed continuious, then it is permisable to use them as conductors. I may be completly wrong, but I have a recolection of that from somewhere. Sorry i'v not got my book on me to check!
 
Isn't there a reg somewhere that if copper water pipes can be confirmed continuious, then it is permisable to use them as conductors. I may be completly wrong, but I have a recolection of that from somewhere. Sorry i'v not got my book on me to check!
well theres 542.2.1 and 542.2.4......
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Gas pipe earth bond.
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
hoover,
Last reply from
chris murphy,
Replies
29
Views
8,191

Advert

TrueNAS JBOD Storage Server

Back
Top