General characteristics | on ElectriciansForums
Discuss General characteristics in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Lincolnshire
When doing mock exams 17th edition the questions that always have me stumped are about general characteristics, I had a question with maximum demand and max current in choices, both seemed feasible answers
Maximum demand is generally the figure you obtain after diversity is applied to the maximum current. For example if you have three 32A ring final circuits their maximum current demand could theoretically be 96A but in reality this is not likely to happen so you apply diversity to come up with a maximum demand figure.
Heres another strange one
7 o/c 4 - Which of the following items does not offer ‘basic’ protection:
a a circuit protective conductor.
b a socket outlet.
c a lampholder.
d equipotential bonding conductors
If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault
Reply to General characteristics in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Thanks mate for the advice, this is just what I was looking for. I think I’ll have to put some thought into the domestic route due to the NVQ and...
Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...