Hi Chris, I don't disagree with what you were saying ( one of your posts seems to have disappeared now) i think we may have been at cross purposes a bit because i might have misinterpreted the way you were using the word "hence".
Are you saying that looking at length of main protective bonding from a voltage drop [Vd=mV/A/m x Ib x L] point of view is not really valid?
Well i asked the question of the IET and here is the answer received - just about a full circle i think!
Hi P
Main Earth bonds (gas ,water etc) should have a value of resistance not exceeding .05ohms, in general terms this would negate the use of a 10mm cable after about 25M after which the conductor size must be increased in order to keep the resistance of the cable below .05 ohms. This is a commonly misunderstood arrangement and contractors constantly fit 10mm bonds in excess of 25M due to a misunderstanding of the regulations
Many Thanks
Richard
Richard Townsend
Senior Engineer
Standards and Compliance
The IET
[email protected]
www.------.org
I
the last 2 posts bring me to ask a question. what are the criteria involved if, say, when doing a CU change and the existing main bonding is 6mm , regarding upgrading to 10mm? various posts have given conflicting views on this. is it acceptable to leave if resistance readings are below a certain figure, or should it be upgraded regardless of anything.
Strange that Pushrod, i spoke to some of his colleagues and they disagreed with th 0.05 ohms and so do i. I can not see how restricting the resistance to 0.05 will achieve anything. I believe its his job to update GN3 so may be he can clarify for the new GN3.
Also, the ECA NICEIC and SELECT all agreed, someones wrong
The other point is, if this was the case then why in 701.415.2 refer you to 415.2.2 for the effectiveness of main bonding?
Why does it not say 0.05?
Theres no requirement to keep the touch voltage below 50v in general installations, due to supply impedance, in most cases little current will flow in the bonding(tn tt).
I fail to see what it will achieve.
the last 2 posts bring me to ask a question. what are the criteria involved if, say, when doing a CU change and the existing main bonding is 6mm , regarding upgrading to 10mm? various posts have given conflicting views on this. is it acceptable to leave if resistance readings are below a certain figure, or should it be upgraded regardless of anything.
but that does not really answer the q. my take is that if the bonding conductor is capable of withstanding the likely fault current for an excess of 0.4 secs. then it is adequate. but would you replace 6mm with 10mm regardless?This is my point, take a TT fault current, it may be quite low due to Ra, so the voltage drop will mainly be at the electrode, so the voltage dropped across R2 will be very low, hence the touch voltage will be low.
Take a TN with a low supply impedance, you could quite easily drop more than 50 V across R2, and have a high touch voltage, hence the 0.4 disconnection time at 230 v.
So if im dropping 80v across R2, assuming little current flow through the bonding conductor what is the purpose a resistance of 0.05.
Do you design your installations to ensure a touch voltage below 50V?
The 50 v rule is additional protection, where at 230v 0.4 disconnection requires supplementing.