but that does not really answer the q. my take is that if the bonding conductor is capable of withstanding the likely fault current for an excess of 0.4 secs. then it is adequate. but would you replace 6mm with 10mm regardless?
Mind the whole of this section (701.415.2) is entitled "supplementary equipotential bonding" and (iii) at the bottom of it says "all extraneous-conductive-parts of the location are effectively connected ... then there is the note referring to 415.2.2 for the assessment of whether parts (rather than a part) are effectively connected to the MET so it could be meaning that they are supplementary bonded and not actually be meaning the mpb, hence the reference... ?The other point is, if this was the case then why in 701.415.2 refer you to 415.2.2 for the effectiveness of main bonding?
.
Mind the whole of this section (701.415.2) is entitled "supplementary equipotential bonding" and (iii) at the bottom of it says "all extraneous-conductive-parts of the location are effectively connected ... then there is the note referring to 415.2.2 for the assessment of whether parts (rather than a part) are effectively connected to the MET so it could be meaning that they are supplementary bonded and not actually be meaning the mpb, hence the reference... ?
Spoke to IET the other day, now Richards colleague has a differing opinion. He agrees with what ive stated and agrees some clarification in the new GN3 would be useful.
Ive also sent an email, but no reply as yet.
Yep the old 2 answers thing again lol at least it is a fairly minor point i suppose. I still have not had an answer to my 2nd question either. Be very interested to see what they reply to you. Maybe they are all going to go down the pub and have a chat about it