is that circuit protected by RCD if not suppose you could parallel two cables together making sure thay are same csa
 
why do you say only option is a 2 way cu jason, surely you could use a spare way on existing cu as long as it was on an rcd????
 
Last edited by a moderator:
how about combining your 2 AC strings into an AC isolator? 2cables into a terminal, one out. go for an oversized isolator, say a 64amp.
 
it's been discussed on here at length that solar needs to be on it's own isolator, been best practice for sometime and you will have problems on your assessment if it goes on a shared RCD.
best way is to wire it so you can totally avoid RCDs

we were all novices once, sorry your experience on here hasn't been very good
 
Look up the threads on here about shared RCDs, if you have about 2 hours to read them.

It to summerise for you Solar PV should be on it's own RCD, that is if it needs one at all.
 
in that case I'm with you. split the tails into a henley block and put in a small CU, say a garage unit. you can use 16mm tails for the garage board.
 
i do now yh then why is all my course note got a lead from the final ac isolator to cu
i did my course in september last year, my instructor said if there is a spare way use it as long as its rcd protected
 
Welcome to Solar nightmare, dont forget your paper trail, your H&S, overstay forms, survey forms, photos, structual reports, handover forms, commission forms, audit forms, the list is longggggggggg.
 
reg 712.411.3.2.1.2 where the pv convertor is, by construction not able to feed dc fault currents into the electrical installation, an rcd of tybe b according to iec 62423 is NOT required
 
Thats for DC leakage, some inverters will trip the RCD, so thats why they have changed the rules.
The DTI guide and IET regs dont really gel
Also type B RCD are expensive and wont be in a standard fuse board
 

Reply to generation meter installation in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

On a 20kw generator can you connect the 30AMP plug to one service panel and the 50amp plug on a seperate service panel? I have two service panels...
Replies
0
Views
215
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
191

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top