I have 2x inverter domestic installation and need some advice on the meter position.
In order to meter generation from both inverters, and both inverters needing a separate MCB, I need to place the meter before a 2 way CU. Would the correct approach to be take tails directly from a henley block to the generation meter, then from the meter to a dedicated 2 way dedicated CU.

What do others do on these jobs?
 
We would put an isolator between the henley block and the gen meter, then the dedicated cu, then two isolators (one each) etc..
 
Same method's good for microinverters, where there is more than one radial circuit feeding several inverters eg on differing roofs
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gr7

-
Joined
Location
Hampshire
Website
https://www.silverstreamsolar.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Silverstream Solar Limited

Thread Information

Title
Generation meter position for multiple inverter installs.
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
gr7,
Last reply from
edexlab,
Replies
3
Views
3,118

Advert

TrueNAS JBOD Storage Server

Back
Top