gr7

-
Joined
Sep 28, 2010
Messages
120
Reaction score
3
Location
Hampshire
I have 2x inverter domestic installation and need some advice on the meter position.
In order to meter generation from both inverters, and both inverters needing a separate MCB, I need to place the meter before a 2 way CU. Would the correct approach to be take tails directly from a henley block to the generation meter, then from the meter to a dedicated 2 way dedicated CU.

What do others do on these jobs?
 
We would put an isolator between the henley block and the gen meter, then the dedicated cu, then two isolators (one each) etc..
 
Same method's good for microinverters, where there is more than one radial circuit feeding several inverters eg on differing roofs
 

Reply to Generation meter position for multiple inverter installs. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
491
  • Question
Thanks guys, that was my alternative thought, as I am running a cat 5 cable for Internet so it has crossed my mind to run another one for the CT...
Replies
3
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top