The question is would a spark only bolt the banjo and not use a flying lead.but seen it done put it down to lazyness.even when using 3 core armour for earth i still gland earth flying lead at cu.
sorry for mis interpreting your post

Check post no1, this is exactly why I questioned it. Circuits using the armour as the CPC but no fly lead used.
 
I was under the impression that you are no longer supposed to bolt banjos to the case of db's because of compromising ip. Banjos ate supposed to be fitted on inside of db, tag bent back and earth tail bolted to it

Don't know how reliable that is
 
I was under the impression that you are no longer supposed to bolt banjos to the case of db's because of compromising ip. Banjos ate supposed to be fitted on inside of db, tag bent back and earth tail bolted to it

Don't know how reliable that is


IMO it would be just as reliable as bolting through the case without taking of any paint.

Can't see how putting a hole through the case and fitting a bolt is going to mess with its ip rating though
 
also earth tags/banjo,s are only ok for fault currents upto 10KA , so if youve got any large cables that could have fault currents above this your supposed to use glands with integral earth boss
 

Reply to the thread, titled "Gland banjo fitting" which is posted in Electrician Talk | All Countries on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top