Global Insulation resistance <1MΩ but individual circuits are all > 1MΩ | on ElectriciansForums

Discuss Global Insulation resistance <1MΩ but individual circuits are all > 1MΩ in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,301
Reaction score
6,540
Location
Gloucestershire
With regards the title is the reason for this because the circuits are all in parallel?

I am talking in relation to a L/N - E test.

If Rt = global resistance for whole CU and R1, R2, R3 = L/N - E resistance for each circuit then am I right with the following:

1/Rt = 1/R1 + 1/R2 + 1/R3

So basically even if the global L/N-E IR test is < 1MΩ, that doesn't automatically mean that an individual circuit is < 1M Ω?
 
correct. bear in mind also that you may have parallel paths due to earthing and bonding etc. simplified, if you have 3 circuits, each 3 Meg, then your global will be 1 Meg,
 
With regards the title is the reason for this because the circuits are all in parallel?

I am talking in relation to a L/N - E test.

If Rt = global resistance for whole CU and R1, R2, R3 = L/N - E resistance for each circuit then am I right with the following:

1/Rt = 1/R1 + 1/R2 + 1/R3

So basically even if the global L/N-E IR test is < 1MΩ, that doesn't automatically mean that an individual circuit is < 1M Ω?
If the global reading is 1M ohm,no cct could be less than that if they are all in parallel,if that's the question. Regards,S
 
I seem to recall as a rule of thumb that the total resistance will always be lower than the lowest individual value. you are right that the reason is because they are all in parallel with each other.

Compliance wise, the >1MOhm is for the installation, not individual circuits.
 
I seem to recall as a rule of thumb that the total resistance will always be lower than the lowest individual value. you are right that the reason is because they are all in parallel with each other.

Compliance wise, the >1MOhm is for the installation, not individual circuits.
So if I had 10 circuits and each of the circuits had 9MΩ of resistance L/N-E, the global IR would then be 0.9MΩ and therefore a fail?
 
So if I had 10 circuits and each of the circuits had 9MΩ of resistance L/N-E, the global IR would then be 0.9MΩ and therefore a fail?
it would not be a fail. as long as each cct. is > 1Meg, it's a pass, but it is advised to investigate any circuit < 2 Meg.
 
No,because you can,t divide by 10,use 1/R =1/r+1/r2+.......etc.S
That is the formula I used. It works out to 0.9M Ω . I'm not sure where you got divide by 10 from, that has nothing to do with this formula.
 
it would not be a fail. as long as each cct. is > 1Meg, it's a pass, but it is advised to investigate any circuit < 2 Meg.
So if each of the 10 circuits tested as 1MΩ, which is a pass. The global IR would be 0.1M Ω .
Would you still class this as a pass?
[automerge]1570801798[/automerge]
Reading reg 643.3.2 it does seem to state that the consumer unit AND each circuit have to be >1M Ω . Therefore 9MΩ on each of 10 circuits would be a fail! Blimey, doesn't sound right.
 
All the circuits at 9M would be OK, but whatever was causing the <1M reading would be an issue.
But that's just it DPG...

1/9 x 10 = 1.1111 recurring

therefore Rt = 1 / 1.111 recurring = 0.9 MΩ

There is nothing specifically causing the 0.9MΩ, there is nothing wrong, this is just what the resistance is with 10 circuits in parallel each with 9M Ω IR.
 
This theoretical situation would be extremely unlikely in my experience, to have all circuits over 1MOhm but the total under. More likely that one or more circuits would be pulling the total readings down due to faults.
 

Reply to Global Insulation resistance <1MΩ but individual circuits are all > 1MΩ in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
359
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top