I shall be replacing my dual RCD CU, for a all RCBO populated CU. A question or two about technique for IR testing.

For the IR test, I've read here before that a global IR test is preferable. With older types of RCBO's that wasn't possible, without disconnecting cables, which ended up with the testing of each individual circuit.

I'm installing a Hager CU, with their miniature ADA RCBO. The MI state an IR test can be carried out on the RCBO terminals, circuit connected with the RCBO turned off. As I've a few different sorts of luminaire connected, I will be doing live/neutral to to earth.

How do you carry out such a test? I've seen some stackable MFT leads, so you can combine live & neutral together?
 
There is a neutral lead from the rcbo to the neutral bar.
I always use dual module rcbo, s (Hagar or GE) where space allows. Single module only where space restricted. A CU with dual module rcbo, s is the easiest CU to install that has ever been invented. The dual module buzz bar means no neutral fly leads. A joy to work with.
 
I always use dual module rcbo, s (Hagar or GE) where space allows. Single module only where space restricted. A CU with dual module rcbo, s is the easiest CU to install that has ever been invented. The dual module buzz bar means no neutral fly leads. A joy to work with.

Not readily available here in England.
 
Yes, but none of them fit a UK-style CU busbar arrangement do they?

We have never had problems getting DP RCBO as standard fitting for a caravan supply, the problem if finding RCBOs for a CU that are neutral switching, but thankfully now a few are (Wylex, Crabtree, Fusebox).

Doing away with flying leads and simply having a neutral busbar would be the answer, but that is not likely here for some time I suspect...
 
Is a neutral busbar worth the additional space required for 2 module RCBOs?

Would those Hagar RCBOs have any benefit over Crabtree, Wylex or Fusebox 1P+N single module RCBOs in a domestic application, other than flylead?
 
Yes, but none of them fit a UK-style CU busbar arrangement do they?
Yes the do, and use a 13mm pitch dual busbar: A9XPH224 | Schneider Electric Acti 9 2 Phase Busbar, 24 Module, 415V, 18mm Pitch | RS Components - https://uk.rs-online.com/web/p/busbars/7762724/
[ElectriciansForums.net] Global IR testing on RCBO populated CU
 
Last edited:

A wylex enclosure and main switch. Hager devices and Schneider bus bar!

Mixing and matching is not allowed here now.

As above, no major U.K. supplier has a CU with that sort of arrangement. Possibly SBS, but I’d rather use a manufacturer where parts will be more likely to be readily available long term and available locally on the shelf.
 
Would those Hagar RCBOs have any benefit over Crabtree, Wylex or Fusebox 1P+N single module RCBOs in a domestic application, other than flylead?
For the typical UK case where N is very much at a low potential to E by design and installation verification, then no.

They seem to bo common in the EU where they have TT as the norm and perhaps traditionally did not have N as near Earth potential. Either as historically it was more like a split-phase supply taking 2 of a 3-phase line set, or for whatever reason they demanded over-current protection on the N side.

The "neutral switching" 1P+N RCBO you see here will detect and isolate an earth fault that happens via the N side, but they do not detect over-current on that side as that is not a UK requirement going back a long, long way. Even when the 13A plug design was introduced in the 40s it was line-side fuse only as installations could be trusted to have N approx E in potential.
 

Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top