I shall be replacing my dual RCD CU, for a all RCBO populated CU. A question or two about technique for IR testing.
For the IR test, I've read here before that a global IR test is preferable. With older types of RCBO's that wasn't possible, without disconnecting cables, which ended up with the testing of each individual circuit.
I'm installing a Hager CU, with their miniature ADA RCBO. The MI state an IR test can be carried out on the RCBO terminals, circuit connected with the RCBO turned off. As I've a few different sorts of luminaire connected, I will be doing live/neutral to to earth.
How do you carry out such a test? I've seen some stackable MFT leads, so you can combine live & neutral together?
Yes, but none of them fit a UK-style CU busbar arrangement do they?
We have never had problems getting DP RCBO as standard fitting for a caravan supply, the problem if finding RCBOs for a CU that are neutral switching, but thankfully now a few are (Wylex, Crabtree, Fusebox).
Doing away with flying leads and simply having a neutral busbar would be the answer, but that is not likely here for some time I suspect...
Is a neutral busbar worth the additional space required for 2 module RCBOs?
Would those Hagar RCBOs have any benefit over Crabtree, Wylex or Fusebox 1P+N single module RCBOs in a domestic application, other than flylead?
Yes the do, and use a 13mm pitch dual busbar: A9XPH224 | Schneider Electric Acti 9 2 Phase Busbar, 24 Module, 415V, 18mm Pitch | RS Components - https://uk.rs-online.com/web/p/busbars/7762724/
A wylex enclosure and main switch. Hager devices and Schneider bus bar!
Mixing and matching is not allowed here now.
As above, no major U.K. supplier has a CU with that sort of arrangement. Possibly SBS, but I’d rather use a manufacturer where parts will be more likely to be readily available long term and available locally on the shelf.
For the typical UK case where N is very much at a low potential to E by design and installation verification, then no.
They seem to bo common in the EU where they have TT as the norm and perhaps traditionally did not have N as near Earth potential. Either as historically it was more like a split-phase supply taking 2 of a 3-phase line set, or for whatever reason they demanded over-current protection on the N side.
The "neutral switching" 1P+N RCBO you see here will detect and isolate an earth fault that happens via the N side, but they do not detect over-current on that side as that is not a UK requirement going back a long, long way. Even when the 13A plug design was introduced in the 40s it was line-side fuse only as installations could be trusted to have N approx E in potential.