AlanWirral
Well a few weeks back a mate of mine called to ask me to do a job for him. Basically fitting an extractor fan in a bathroom.
I was too busy so the 'Builder' doing the bathroom got a 'Spark' to come and do it for them. Now today i got a call to come and have a look at the job as they didn't think it was right
When i got there i was told there were two basicaly 'Young lads' doing the work and they had wrecked the ceiling and smashed an expensive lampshade on the landing
Walking up the stairs i see the cover off the pendent on the landing and a new 2 core 1.5mm T&E wired into the switched live so they then run it in the loft space (over the joists) and down the inside of the bathroom wall, drilled through to a surface mounted switched fused spur on the outside of the bathroom above the door.
Then from that into the loft space (over joists) down the wall to a ceramic air vent that had been smashed from a rectangle into a resembled 'round' hole. What was more shocking is the fan needs to be selv as it can be touched from the bath easily AND the loft hatch is in the bathroom with the existing fitting (pendent) right next to it!
Going to rewire and isolte accordingly with IP rated DL's and a ELV fan fed from above. How the hell does this stuff still go on
I was too busy so the 'Builder' doing the bathroom got a 'Spark' to come and do it for them. Now today i got a call to come and have a look at the job as they didn't think it was right
When i got there i was told there were two basicaly 'Young lads' doing the work and they had wrecked the ceiling and smashed an expensive lampshade on the landing
Walking up the stairs i see the cover off the pendent on the landing and a new 2 core 1.5mm T&E wired into the switched live so they then run it in the loft space (over the joists) and down the inside of the bathroom wall, drilled through to a surface mounted switched fused spur on the outside of the bathroom above the door.
Then from that into the loft space (over joists) down the wall to a ceramic air vent that had been smashed from a rectangle into a resembled 'round' hole. What was more shocking is the fan needs to be selv as it can be touched from the bath easily AND the loft hatch is in the bathroom with the existing fitting (pendent) right next to it!
Going to rewire and isolte accordingly with IP rated DL's and a ELV fan fed from above. How the hell does this stuff still go on