Got a call from a mate earlyer...

A

AlanWirral

Well a few weeks back a mate of mine called to ask me to do a job for him. Basically fitting an extractor fan in a bathroom.

I was too busy so the 'Builder' doing the bathroom got a 'Spark' to come and do it for them. Now today i got a call to come and have a look at the job as they didn't think it was right :rolleyes:

When i got there i was told there were two basicaly 'Young lads' doing the work and they had wrecked the ceiling and smashed an expensive lampshade on the landing :confused:

Walking up the stairs i see the cover off the pendent on the landing and a new 2 core 1.5mm T&E wired into the switched live :D so they then run it in the loft space (over the joists) and down the inside of the bathroom wall, drilled through to a surface mounted switched fused spur on the outside of the bathroom above the door.

Then from that into the loft space (over joists) down the wall to a ceramic air vent that had been smashed from a rectangle into a resembled 'round' hole. What was more shocking is the fan needs to be selv as it can be touched from the bath easily AND the loft hatch is in the bathroom with the existing fitting (pendent) right next to it! :rolleyes:

Going to rewire and isolte accordingly with IP rated DL's and a ELV fan fed from above. How the hell does this stuff still go on :mad:
 
And SELV!

Extractor fans installed within zone 1 must be at least IPX4.
Extractor fans installed within zone 1 must be fitted with 12v SELV motors with the SELV transformers and isolators fitted outside of zone 0, 1 & 2
do you have trhe reg. no. for that?
 
And SELV!

Extractor fans installed within zone 1 must be at least IPX4.
Extractor fans installed within zone 1 must be fitted with 12v SELV motors with the SELV transformers and isolators fitted outside of zone 0, 1 & 2

where did you find that from .confused some more still ;-)
 
i reserve my opinion until i've checked. too late tonight . zebedee says time for bed BOOOOOOOINGGGGGGG
 
OSG table 8.1 (page 70) lists under Zone 1 some equipment that can be mains voltage equipment with minimum IPX4 / IPX5 (Jets) “...mains voltage, fixed, permanently connected equipment allowed: whirlpool units, electric showers, shower pumps, ventilation equipment...”.

I’m guessing an extractor fan fits comfortably under the category “ventilation equipment” ?


OSG 7.2.5 states RCD’s are required for circuits containing a bath or shower. :)
 
No RCD protection and touchable from the bath

If you alter an existing None RCD circuit to add to it dont you need to add RCD to comply and also check that both main bonding is upto date too to comply. If there is RCD i would be happy with fixed 240 but as others have said 12v isnt much more and normally locate the tranny next to the isolator position etc.
 