Grade A Fire Detection Advice/Installer Required | on ElectriciansForums

Discuss Grade A Fire Detection Advice/Installer Required in the UK Electrical Forum area at ElectriciansForums.net

ahhaah

DIY
Joined
Nov 30, 2024
Messages
4
Reaction score
0
Location
London
In my 3 storey house I need to fit a grade A LD2 alarm system. Mains connected grade D currently exists in the correct locations but I guess because they are not fed by FP cable I will need to rewire to the new detectors I'll need to purchase, which I am capable of doing.

What I can't do is connect it all up to the control panel and the control panel to the consumer unit. I will also need a certificate. For this I would hire someone.

Questions:

Does the above sound like a reasonable way of lowering labour costs that an electrician can work with?

Does all FP cable need to be enclosed in trunking (even if inside a cupboard or in the loft)?

Is the interlink cable separate?

Any advice for how to get this sorted as low cost as possible? Happy to receive quotes (NW London).
 
In my 3 storey house I need to fit a grade A LD2 alarm system. Mains connected grade D currently exists in the correct locations but I guess because they are not fed by FP cable I will need to rewire to the new detectors I'll need to purchase, which I am capable of doing.

What I can't do is connect it all up to the control panel and the control panel to the consumer unit. I will also need a certificate. For this I would hire someone.

Questions:

Does the above sound like a reasonable way of lowering labour costs that an electrician can work with?

Does all FP cable need to be enclosed in trunking (even if inside a cupboard or in the loft)?

Is the interlink cable separate?

Any advice for how to get this sorted as low cost as possible? Happy to receive quotes (NW London).
Do nothing without the express permission, and following all lawful orders, of the electrical contractor/fire alarm installer.
 
I would be employing someone from the outset to do all the installation work, the questions you are asking suggest you are not competent to be doing this.
 

Reply to Grade A Fire Detection Advice/Installer Required in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
603
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
353
ESP - https://www.espuk.com/# is the company you are referring to part of Scolmore
Replies
2
Views
399