hi all i have changed 6x gu10 downlights in a kithchen as the down lights befor kept blowing there were LV.

what may cause the lamps to blow regualy eg only 3-4 hours of being on? all suggestions would be grat
 
Are you sure they are only lasting a few hours?...customers often say they have only lasted a short time when in reality they have got mixed up with what has been replaced. A loose connection serious to cause lamp failure would almost certainly produce noticable flickering.
I would still suggest it is lamps..(see robsparkys post)....try a different batch of a quality brand and get the customer to keep a plan of which lamps blow and when.
 
hi all just to let u no i have been back and its not the lamps. they are fine and so are the fittens.. who ever wired it befor have done some thing wrong.

i have 230V between L&N
230V between N&E
0V between L&E
 
hi all just to let u no i have been back and its not the lamps. they are fine and so are the fittens.. who ever wired it befor have done some thing wrong.

i have 230V between L&N
230V between N&E
0V between L&E

Wrong polarity....the N and L are reversed......needs rectifying but wont affect lamp life.
 

Reply to the thread, titled "gu10 mains lamp blowing" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top