Hey up, friend of mine has a 4575 W dryer, big american thing. Now it says in the manual that it needs its own 30A supply with an isolating switch. Am i right in saying it will need to be fed from a 32A breaker from the mains board in 6mm ? or will 4mm cover it ? Its about a 10 metre run under the kitchen units. He's pretty keen on just flexing it up and plugging it into the kitchen ring!!
Struggling a bit with the cable calcs.
Cheers
 
Gravid as with that wattage +19.89 amp it cant be plugged it. I would recon a 32A Rcbop clipperd direct (method c ) under the worktop with a 4mm cable would be fine. then put it on an unnmarked cooker control unit as your local isolation
 
let him plug it up and watch the fuse pop in the plug top. that thing is gona drag around 20amps. Yes it needs its own circuitminimum of 25A supply(not sure iof you can get 25A MCB'S. You can in Eurpe) but 30A is more likely.
 
There may not be any need for rcd protection if there is a spare way in the CU and the cable is not buried in a wall less than 50mm from the surface.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gravid

Arms
-
Joined

Thread Information

Title
Hard Wired Dryer
Prefix
N/A
Forum
Electrical Appliances & Whitegoods Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Gravid,
Last reply from
lurch,
Replies
8
Views
1,768

Advert

Back
Top