Hard Wired Dryer | on ElectriciansForums

Discuss Hard Wired Dryer in the Electrical Appliances Forum area at ElectriciansForums.net

Gravid

-
Arms
Joined
Jan 5, 2009
Messages
342
Reaction score
34
Hey up, friend of mine has a 4575 W dryer, big american thing. Now it says in the manual that it needs its own 30A supply with an isolating switch. Am i right in saying it will need to be fed from a 32A breaker from the mains board in 6mm ? or will 4mm cover it ? Its about a 10 metre run under the kitchen units. He's pretty keen on just flexing it up and plugging it into the kitchen ring!!
Struggling a bit with the cable calcs.
Cheers
 
Gravid as with that wattage +19.89 amp it cant be plugged it. I would recon a 32A Rcbop clipperd direct (method c ) under the worktop with a 4mm cable would be fine. then put it on an unnmarked cooker control unit as your local isolation
 
let him plug it up and watch the fuse pop in the plug top. that thing is gona drag around 20amps. Yes it needs its own circuitminimum of 25A supply(not sure iof you can get 25A MCB'S. You can in Eurpe) but 30A is more likely.
 
Ok thanks lads,
One more thing, in this scenario would you get the current carrying capacity from table 6F in the OSG?
 
There may not be any need for rcd protection if there is a spare way in the CU and the cable is not buried in a wall less than 50mm from the surface.
 
Last edited by a moderator:

Reply to Hard Wired Dryer in the Electrical Appliances Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

By code the washing machine needs its own 20 amp single pole GFCI circuit, the dryer needs a 30 amp double pole breaker and using # 10 wire. Your...
Replies
1
Views
793
Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
460

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top