UK Hardwiring an induction hob

The cable is a direct 8 metre run under floorboards
So not a long run then .you have a socket on your cooker switch .Best bet is to get an electrician in to work out the diversity and if you can replace the cooker switch with a normal switch unless of course you need it /are using it and that would help with loading .diversity is just a factor that seems to work and has done for years but only for normal use .if your using socket for a kettle say and your cooking xmas dinner there's always a chance the 32 mcb will trip.best to get an electrician in to have a look .they may be able to run in a new cable for oven although your rcd side of board is full .they may be able to fit a different type of rcbo on other side
 
if you're using the socket for a kettle say and your cooking xmas dinner there's always a chance the 32 mcb will trip.

We have never used the socket so that shouldn't be a problem.
 
Please help...Had an AEG Double Oven Built-under, go wrong. AEG sent replacement oven & when engineers went to swap over, they stopped. I'm now left with an unconnected oven. They are saying Currys installation team shouldn't have connected induction hob & oven on same circuit , & for safety they would not do it. They said I need a new hob that can be wired into 13amp wall socket. Currys say the two can be wired together & do not want to take responsibility. I'm left with a ruined Easter!
 
It may be ok to have both hob and oven on the same circuit, as you can see from the thread you've joined. However, if the engineers won't do it then you'll have to get an electrician out.
Why don't you give your approx location and someone on the site might be near by and happy to come out today... double time I expect though. Unlikely, but worth a shot.
 
Where in Uk? Maybe a forum member can help you out.
IP address suggests near Norwich? Is that right?


It all really depends on the load of both the oven and hob together, compared with the supply circuit size.
There is an equation, called diversity, that means the load is much less than the maximum of both added together.

Even if it is slightly more, the worst that would happen is the circuit breaker would trip.

Was it AEGs own engineer?


I’ve just connected a new 5 ring AEG to an existing circuit with a double oven. No problems at all.



With a username like Snow White…. I guess you’re feeling a little Grumpy just now?? 😁


Sorry
 
The electrician who came to connect the hob put a JB behind the oven and wired both units together. He did not alter the circuit breaker or touch the wall switch.

I did query the JB and he (rather shirtily) told me it was perfectly acceptable. I have been using both units, sometimes both at the same time, for a couple of weeks now with no apparent problems.
 
Thanks to all ,who have bothered to reply, I have attached two pieces of report to hopefully clarify the situation we're in!
 

Attachments

  • Screenshot_20250419_104717_PRINT.jpg
    Screenshot_20250419_104717_PRINT.jpg
    45.6 KB · Views: 17
  • Screenshot_20250419_104653_PRINT.jpg
    Screenshot_20250419_104653_PRINT.jpg
    75.5 KB · Views: 14
Where in Uk? Maybe a forum member can help you out.
IP address suggests near Norwich? Is that right?


It all really depends on the load of both the oven and hob together, compared with the supply circuit size.
There is an equation, called diversity, that means the load is much less than the maximum of both added together.

Even if it is slightly more, the worst that would happen is the circuit breaker would trip.

Was it AEGs own engineer?


I’ve just connected a new 5 ring AEG to an existing circuit with a double oven. No problems at all.



With a username like Snow White…. I guess you’re feeling a little Grumpy just now?? 😁


Sorry
I think at this rate I'm needing Doc, for my blood pressure! I have written a reply with screenshot.
 
They certainly have NOT applied diversity, whatever their little report says.

Taking the diversity equation from earlier in this thread, (message #5)

For each appliance, work out total amps....

Hob
7300/230 = 32A
Take 10 off, and add 30% of remainder.... 30% of (32 - 10) = 6.6
Add the 10 back on... 16.6A

Oven
5300/230 = 23A
30% of (23-10) 3.9
Add the 10.... 13.9A

Total load with diversity is 16.6 + 13.9 = 30.5A


That was just a quick count up, and my collegues may have a different method.... but whatever.... theres nothing wrong with doubling up the hob and oven on a 32A 6mm supply
As long as the circuit is RCD protected, theres no reason not to connect.

How you convince them, however, i dont know
 
Hope this helps!
 

Attachments

  • Screenshot_20250419_115235_PRINT.jpg
    Screenshot_20250419_115235_PRINT.jpg
    52.2 KB · Views: 17
  • Screenshot_20250419_115142_PRINT.jpg
    Screenshot_20250419_115142_PRINT.jpg
    50.4 KB · Views: 15
  • Screenshot_20250419_115059_PRINT.jpg
    Screenshot_20250419_115059_PRINT.jpg
    111.3 KB · Views: 16
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Santa,
Last reply from
brianmoooore,
Replies
38
Views
854

Advert

Back
Top