Thanks for the replies folks, I guess the main point is should I have it done again or have it plastered over the way it is? Thanks

I think you should ask the electrician to come back and route the cables in the "safe zones" - have you paid him yet?
 
I cant understand the reason behind his method, surely it would have been easier for him anyway to follow the safe zones when chasing out?!!?
 
It will only be a matter of time before a nail or screw damages a cable!

A shelf or something else placed onto the wall.

I bet the person putting them in will not come back for free and repair not only the cable but your decoration plaster etc!!
 
Crikey, that’s a lot of chasing for a light switch! This man must enjoy hard work.

The runs by the door appear to be more than 150mm from the corners so are (just) out of the regulation zones. The horizontal run is compliant.

BUT contrary to what others have said above, IF the circuit is 30mA RCD protected (OP please check if there’s a little test button on the breaker for this circuit in the consumer unit) my understanding is that wiring can be shallow, and unprotected, so it’s not a major departure overall.

I checked Section 522 in detail when I rewired my own house, and wanted to keep some electrically sound, but badly-run existing lighting drops, which were certainly less than 50mm deep. My installation now has 6A/30mA RCBOs on all the lighting circuits. I’m absolutely sure it complies.

My understanding is that new cable installs:

1. MUST be in the ‘safe zones’ but,

2. If the wires are shallow, have no mechanical protection, or are in a partition with metallic structure (regardless of cable depth), that’s fine, but the circuit must be RCD protected, that’s all.

Clearly one can’t be expected to cut a horizontal chase over 50mm deep into, say, a single brick load-bearing wall without the immediate danger not being electrical… :)

ps That said, I think it looks a bit of a pig’s ear, and it's not how I’d have done it, but I’m not convinced it’s grossly non-compliant.
Maybe there was an absolute client prohibition on disturbing ceilings or floors? Or it’s a flat with concrete ceilings and a solid floor?
 
Last edited:
Crikey, that’s a lot of chasing for a light switch! This man must enjoy hard work.

The runs by the door appear to be more than 150mm from the corners so are (just) out of the regulation zones. The horizontal run is compliant.

BUT contrary to what others have said above, IF the circuit is 30mA RCD protected (OP please check if there’s a little test button on the breaker for this circuit in the consumer unit) my understanding is that wiring can be shallow, and unprotected, so it’s not a major departure overall.

I checked Section 522 in detail when I rewired my own house, and wanted to keep some electrically sound, but badly-run existing lighting drops, which were certainly less than 50mm deep. My installation now has 6A/30mA RCBOs on all the lighting circuits. I’m absolutely sure it complies.

My understanding is that new cable installs:

1. MUST be in the ‘safe zones’ but,

2. If the wires are shallow, have no mechanical protection, or are in a partition with metallic structure (regardless of cable depth), that’s fine, but the circuit must be RCD protected, that’s all.

Clearly one can’t be expected to cut a horizontal chase over 50mm deep into, say, a single brick load-bearing wall without the immediate danger not being electrical… :)

ps That said, I think it looks a bit of a pig’s ear, and it's not how I’d have done it, but I’m not convinced it’s grossly non-compliant.
Maybe there was an absolute client prohibition on disturbing ceilings or floors? Or it’s a flat with concrete ceilings and a solid floor?
the route up by the door and the horizontal run above the door are both outside of prescribed zones so, no matter how many RCDs protect the circuit, unless the runs are in earthed metallic conduit, they are non compliant and therefore unacceptable. end of.
 
It sounds to me like the OP should have just asked the neighbour to do it, at least then it would have complied.

What a bodge job. OP where did you hear about this electrician? Are they part of a Part P scheme? I'm afraid my advice would be DON'T get them back. Find a reputable electrician to carry out the repairs to this shoddy workmanship.

:thumbsup
 
This thread just goes to show how poorly the "safe" zones are publicised (had to educate a builder just yesterday), how little some sparkies know, and how on earth is Joe Public supposed to know??
 
This thread just goes to show how poorly the "safe" zones are publicised (had to educate a builder just yesterday), how little some sparkies know, and how on earth is Joe Public supposed to know??
Kitchen fitters, general builders, labourers et cetera
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Has my electrician done a dangerous wiring job?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
74

Advert

Thread statistics

Created
Homervanderjazz,
Last reply from
Des 56,
Replies
74
Views
11,090

Advert

Back
Top