Have I possibly damaged the underfloor heating mat? | on ElectriciansForums
Discuss Have I possibly damaged the underfloor heating mat? in the UK Electrical Forum area at ElectriciansForums.net
London
So I’m fitting an electric underfloor heating mat by pro warm. I was testing it for continuity between L N and got 88ohms which is what it should be according to the instructions.
It says to do IR test at 500V but it doesn’t say between which colours. So I did L N and got 0.00ohms. Have I damaged the mat? I realised after maybe I shouldn’t have done that. I did L E and N E and it was >1049Mohms.
I looked at the instructions and it doesn’t say which cables to IR test between which was annoying.
You wont damage the mat by sending 500 or even 1000V from the megger down the live and neutral wires, the current from these meters is so low it wont do anything, I think its 1mA max.
On a similar note I've fitted loads of these mats over the years and tested each on before and after and never encountered any issue/fault anywhere. So I lay my own mat in my bathroom the other year and don't bother with the testing as its always been ok in the past, lay my own tiles very carefully and when I come to power up the mat for the first time - zilch. Must have been faulty from the factory, unbelievable.
Luckily I'm currently re modelling that bathroom and have just taken the floor up, this time I'll be a lot more through.
The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from each other, they are connected together, so what further instruction is needed?
Reply to Have I possibly damaged the underfloor heating mat? in the UK Electrical Forum area at ElectriciansForums.net
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
    • Winner
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...