Gents, in need of your experience/knowledge.

Im working in maintenance at a student accommodation. ( over 900 rooms, over 60 boards )

The buildings need their periodic inspection and testing.

Im trying to be as less disruptive as possible so am just turning the circuits off under test. However, im finding this really uncomfortable, what with the arching and cpcs squeezed behing the line cables. I have asked permission to turn the board off, but this isnt really an option as the rooms all have fridges in and the students are forever studying. My question, can i obtain R1 + R2 by taking my highest Zs reading, calling the Elec board up and getting a true reading of Ze, and making a calculation. I just cant see how this would be good enough to put on a cert as the board will only give me a Ze from the intake room for starters. Plus the fact Zs will have parallel paths. Before i get abused, yes i have my 2395, although my experience in testing is limited. ( Thrown in at the deepend )

Thanks guys.

Tom
 
Please make sure you do a "soft test" 250V IR L&N to earth. With the amount of laptops, mobile phones, Ipods, Sky hubs etc in these places you could open up a world of financial problems for a simple mistake on this scale.

That reminds me. I've got 4 blocks of student accommodation to do an EICR upon in the next few months. Each block is 9-14 stories tall! Never seen inside, no idea what is going to pop up? We just have to be methodical, planned, informed and inform others (tenants,24/7 alarm company, fire brigade if need be etc, cctv security room, any other staff working in the building/s).

God luck with it and ask any questions you have, sure we will all give you support on a job this size. It is not an every day thing.
 

Reply to Heeeellpp!!!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
384
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top