going by the rating plate on the OP's post. it says 230/380. had similar on a farm. installer wired it in delta on 415V. it lasted 20 minutes.
Discuss HELP 3 phase masonary saw wiring in the Talk Electrician area at ElectriciansForums.net
Perhaps it would have bee a good idea to use a S/D starter in the first place, staring something in Delta is in my book asking for a burn out, after all that's why some motors aren't started DOL or in Delta,going by the rating plate on the OP's post. it says 230/380. had similar on a farm. installer wired it in delta on 415V. it lasted 20 minutes.
A bit of motor theoryI must be missing something obvious here
Have you got a locked rotor?hello got a problem with my 3phase masonary saw somebody has wired it up I don't think it's correct because the blade sometimes spins backwards and often doesn't start when turned on without a spin first makes a buzzing sound and does nothing it's also getting really hot. I will attach pics of the wiring diagram and the actual wiring on the saw
A star delta starter will in effect put 380/root3 volts across each winding, on start up, wouldn't it? into delta after a predetermined time the starter would change over and slap 380/400 across each winding.Wht would a star delta starter burn the motor out?
pete.you're missing the point.the motor is designed for 230V across each winding.on a 415 3 phase supply that's only in star. delta would put 415 on each winding. can only be delta on a 230V p-p supply.A star delta starter will in effect put 380/root3 volts across each winding, on start up, wouldn't it? into delta after a predetermined time the starter would change over and slap 380/400 across each winding.
The only way delta would burn out the motor would be because the mechanical load is to much, thus causing the winding's to overheat and burn out, purely a mechanical problem, that's why 3 phase squirrel cage motors are sometime started via a S/D starter, Star low voltage high torque Delta higher voltage lower torque due to the increased speed on star start up.
I agree Starting and running in Delta would probably burn the winding's out, but this will be due to overheating at a higher torque, nothing to do with the winding getting 230 v or 380 v, perhaps Westward's comment of more Motor knowledge is required is a bit wrong don't you think?
A special Motor then?pete.you're missing the point.the motor is designed for 230V across each winding.on a 415 3 phase supply that's only in star. delta would put 415 on each winding. can only be delta on a 230V p-p supply.
Reply to HELP 3 phase masonary saw wiring in the Talk Electrician area at ElectriciansForums.net