help compleating domestic electrical installation certificates

a few questions can anyone please help.

on the second page particulars of installation at the origin, it states number of smoke alarms do you fill this in if you have fitted the smoke alarms yourself or do you still fill it in i.e put down 2 even if their is 2 smoke alarms in the house.

under main switch or circuit-breaker if it is a sub main do you put the main switch in this case a 61009 rcd or the mcb 60898 type 2 feeding the board.

is the max zs permited for a 60898 type 2 the same as a type b.

insulation resistance testing line/line what is this live to live on a ring main only.

:confused:
 
Only the work you cover! If you install a single circuit then NO, if you do a board change then YES!

Main Switch will be the 61008 Rcd on a sub board.

60898 type 2 ?? Do you mean 3871 type 2 ? If so then NO!

IR Line/Line, I thought that was for 3 Phase only...!?

Cheers
 
Last edited:
1) I have never seen smoke alarms detailed under the particulars of the installation ? What is the design of your cert?
2)Main switch or circuit breaker refers to the main switch or circuit breaker for the INSTALLATION not the submain. IE main switch on incoming consumer unit so 61008 by the sounds of it
3)type 2 ? sounds like a BS3871 MCB you have there not a BS60898
4)I R line to line refers to three phase only not applicable for ring circuits


Spud
 
5 s if cabling run surface and supply outlet rated greater than 32A. (which i assume it is if 40A) is it a shower or cooker? only 0.4 s if cabling behind plaster or in partition @ depth less than 50mm
 
1) I have never seen smoke alarms detailed under the particulars of the installation ? What is the design of your cert?

Spud the NIC forms have a box for that in particulars of the installation , I've always filled it in whether or not they were installed by me.
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
mcm,
Last reply from
robd,
Replies
10
Views
2,928

Advert

Back
Top