O

olsonn

I am trying to do some individual circuit testing ahead of my 2391 practical, but I am having a problem with final ring circuits. Radial circuits aren't a problem, but when you look in all the guidance including GN3 it only deals with lighting circuits. Do you have to join all 4 live ends together? I am obviously doing something wrong as the 3 step continuity of ring final circuits is, spot on as is the R1+R2, but I am getting 0.00 for IR.
 
If the resistance between L/N are o.k and also between L/E you can edge your bets N/E will be aswell!

you hope. if no loads connected, L/N will read good. L/E will also read good even if you short N/E
 
well, there i was , diggin that hole , hole in the ground, so big and round and deep it was. it's not there now, the ground's all flat, and beneath it is the bloke in the bowler hat. ( good place for LABC )
 
Well I took the advice offered and disconnected both ends of the ring at the board. Put the L N and CPC from one end in to seperate choc blocks and tested using the other end. Tested between N and CPC and got 9.06, then tested between L and CPC and got 9.06 not great but a pass. Problem is I tested between L and N and got 0.00.


What am I doing wrong, or am I doing right and the circuit is wrong??
 
Well I took the advice offered and disconnected both ends of the ring at the board. Put the L N and CPC from one end in to seperate choc blocks and tested using the other end. Tested between N and CPC and got 9.06, then tested between L and CPC and got 9.06 not great but a pass. Problem is I tested between L and N and got 0.00.


What am I doing wrong, or am I doing right and the circuit is wrong??
9.06 What? Megohms?
 
This is what I do......

First make sure all appliances are unplugged, any fuse spurs turned off (this would give you a 0.26ish result, from reading between the neon)

One crocodile clip on both live conductors, the other on the Neutral conductors. Test. Hopefully >99.9

Repeat test for Live/Earth and Neutral/Earth.

Done. Although you could save time, by doing as what someone said above, using the screw in the MCB, and the busbars. If your really special you can IR test the whole installation at once. Making extra sure, you disconnect any equipment suspect to high voltages.
 

Reply to Help IR Testing on a ring final circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
492
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
971
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top