Help needed to review quality of distributer box installation | Page 7 | on ElectriciansForums

Discuss Help needed to review quality of distributer box installation in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 22, 2018
Messages
6
Reaction score
1
Location
Glasgow
Hi everyone,

I just had my distributer box upgraded to an RCD box, and I was wondering if anyone could advise me on the quality of the work done here. I know that changing these boxes is a nightmare to do, and truth be told our wiring was a mess before, but for the price we payed I don't believe there should be electrical tape and exposed wires coming out of the box. Also you can see the housing for the old night electricity box which they have decided to leave and they also chose not to cover the channel with all the exposed wires. I'm just curious to see what this forum's take is on this work, and if it was worth the ÂŁ700 I payed for it.

Thanks!

(This is my first post, so if I am in the wrong category I apologise)
[ElectriciansForums.net] Help needed to review quality of distributer box installation


[ElectriciansForums.net] Help needed to review quality of distributer box installation
 
,

To be honest I'm not sure that's why i put it as a question in the end, i was thinking of eicr classification codes. i just don't see why unlabeled circuits significantly reduces the safety of an installation that's all.

My view is, the customer may turn off something and think they've isolated it. We have the luxury of the correct test gear so we can ensure it's dead, most customers don't.

In the event of a fault, faffing around trying to isolate the correct item could be the difference between no fire and a fire. Or... injury vs. death.
 
Removed from where ?

From the copy of the report that I sent to the OP this afternoon. The VCR that I uploaded to the forum was incomplete insofar that the OPs personal details and address hadn't yet been entered.
 
So... a few days ago I posted this image of what I imagined could be going on beneath the cover:
[ElectriciansForums.net] Help needed to review quality of distributer box installation


And @JK-Electrical revealed this image of the actual work carried out:
[ElectriciansForums.net] Help needed to review quality of distributer box installation


Eerily close!
The number of times I've come across boards like this and advised the customer.. Most don't care
"it works doesn't it?"
"Yep it does for now, give it a while and you'll prob get a free firework display out of it too.."
 
Top work JK! :)

Also, out of interest, I noted you put a C3 for the off peak board as it has a 63A 30ma RCD as Main Switch which feeds 3 x 16A MCB's supplying heaters. . Install is poor obviously lol, but can't see any issue with the selection of devices. What is it that you feel is not compliant with BS7671 with regard to selection ?
 
Top work JK! :)

Also, out of interest, I noted you put a C3 for the off peak board as it has a 63A 30ma RCD as Main Switch which feeds 3 x 16A MCB's supplying heaters. . Install is poor obviously lol, but can't see any issue with the selection of devices. What is it that you feel is not compliant with BS7671 with regard to selection ?

Thank you TJ.:)

Had it been me who did the install, I would have opted for a 100 amp main switch and three RCBOs, my reasoning being that should an overnight fault develop on any of the three heaters, or in any of the circuits supplying them, the homeowner doesn't wake-up one cold winter morning to a freezing flat! My decision is based solely on minimising inconvenience hence the 'improvement recommended' coding.

As an aside, I wouldn't have chosen the Axiom brand in the first place, and would have fitted a better-quality brand such as Hager, Wylex or Crabtree rather than this cheap crap from Toolstation. Given the amount that the customer was charged for this job, there can be no excuse for not fitting RCBOs.
 
Last edited:
Did he replace both boards ie the little one at the bottom and the big one at tge top?
Yes both boards were replaced plus electric shower was also replaced in the bathroom.what i find strange is that the tails were hanging out of the gromits and one of the neutrals was exposed when they had been clearly hidden in the first place also the customer had already said that they had a previous electrician who done shawdy work as they put it and hadnt paid them!!why hadnt they contacted them to tell them about this but instead went onto a forum and tried to slate them !!!
 
Yes both boards were replaced plus electric shower was also replaced in the bathroom.what i find strange is that the tails were hanging out of the gromits and one of the neutrals was exposed when they had been clearly hidden in the first place also the customer had already said that they had a previous electrician who done shawdy work as they put it and hadnt paid them!!why hadnt they contacted them to tell them about this but instead went onto a forum and tried to slate them !!!

Was the electric shower replaced? Don't recall seeing a mention of that in any of the posts thus far.

The OP didn't come onto the forum slating someone, they came on looking for some advice (although I suspect they knew what the answer would be).

What I do find quite interesting is this is your first post on the forums, you're in Glasgow, there's no electrical qualifications in your profile and the excess exclamation marks adding emphasis suggest you might be a little angry at potentially an individual not being paid for doing shoddy work and potentially for that individual getting a slating in public.

So I have to ask... are you the person who did the installation that has been photographed here? Your post makes me think maybe you might be.
 
Yes both boards were replaced plus electric shower was also replaced in the bathroom.what i find strange is that the tails were hanging out of the gromits and one of the neutrals was exposed when they had been clearly hidden in the first place also the customer had already said that they had a previous electrician who done shawdy work as they put it and hadnt paid them!!why hadnt they contacted them to tell them about this but instead went onto a forum and tried to slate them !!!
Was the electric shower replaced? Don't recall seeing a mention of that in any of the posts thus far.

The OP didn't come onto the forum slating someone, they came on looking for some advice (although I suspect they knew what the answer would be).

What I do find quite interesting is this is your first post on the forums, you're in Glasgow, there's no electrical qualifications in your profile and the excess exclamation marks adding emphasis suggest you might be a little angry at potentially an individual not being paid for doing shoddy work and potentially for that individual getting a slating in public.

So I have to ask... are you the person who did the installation that has been photographed here? Your post makes me think maybe you might be.
No i wasn't the one who done the instalation but i was the one who fitted the shower on that job
 

Reply to Help needed to review quality of distributer box installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top