Steve93

-
Trainee
Joined
Apr 23, 2017
Messages
65
Reaction score
15
Location
Southampton
I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?

[ElectriciansForums.net] Help! Never seen this before!


[ElectriciansForums.net] Help! Never seen this before!
 
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.

Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
 
Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
Yes explained clear as day she just put me on hold and then went on to say they can send someone out in 5 weeks.
 

Reply to Help! Never seen this before! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
602
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top