Steve93

-
Trainee
Joined
Apr 23, 2017
Messages
65
Reaction score
15
Location
Southampton
I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?

[ElectriciansForums.net] Help! Never seen this before!


[ElectriciansForums.net] Help! Never seen this before!
 
That's bull...
The incoming equipment is owned by the supply authority. If any danger occurs it's their responsibility.
They may have less interest but that doesn't mean they aren't responsible.

The equipment is old and, especially looking at the ceramics involved, requires an upgrade.
I've had quite a few changed over the years.

You are correct, the incoming equipment is the owned and is the responsibility of the DNO but as I said the earthing is not their responsibility and has not been for some time, it is now being pushed as the responsibility of the consumer. Unless there is a real and present danger, they will not consider it a priority to attend site to look at ‘no earth’. You will find that they are doing the same for lateral mains which they are now pushing to the free holders.
 
[ElectriciansForums.net] Help! Never seen this before!
That's bull...
The incoming equipment is owned by the supply authority. If any danger occurs it's their responsibility.
They may have less interest but that doesn't mean they aren't responsible.

The equipment is old and, especially looking at the ceramics involved, requires an upgrade.
I've had quite a few changed over the years.
 
but as I said the earthing is not their responsibility and has not been for some time, it is now being pushed as the responsibility of the consumer.

Unless I'm much mistaken, distributors are obliged to provide an earth wherever practical as stated in the ESQC regulations, regulation 24 item 4 to be precise.

"(4) Unless he can reasonably conclude that it is inappropriate for reasons of safety, a distributor shall, when providing a new connection at low voltage, make available his supply neutral conductor or, if appropriate, the protective conductor of his network for connection to the protective conductor of the consumer’s installation."
 

And I'm sure that incomplete quote is likely to go on and state it is the consumers responsibility to ensure the installation is earthed, which it is. That doesn't alter the fact the DNO is obliged to provide a means of earthing wherever possible.
 
Although there is nothing dangerous with the the current ISCO equipment currently installed and in fact looks in very good condition for its age a modern insulated head would be inherently safer and with the possibility of a TNC-S connection (area dependant).

I would of probably rang the DNOs emergency No. and stated I could hear fizzing from inside IF I wanted it changed ASAP.

The E.B. lads are usually really helpful if you manage to get them onsite.
 
And I'm sure that incomplete quote is likely to go on and state it is the consumers responsibility to ensure the installation is earthed, which it is. That doesn't alter the fact the DNO is obliged to provide a means of earthing wherever possible.

Correct again. They are obliged to provide a means of earthing but it is the consumers responsibility to Earth his installation.
 
You are correct, the incoming equipment is the owned and is the responsibility of the DNO but as I said the earthing is not their responsibility and has not been for some time, it is now being pushed as the responsibility of the consumer. Unless there is a real and present danger, they will not consider it a priority to attend site to look at ‘no earth’. You will find that they are doing the same for lateral mains which they are now pushing to the free holders.
The earthing isn't the actual issue for contacting the authority. It's the age and suitability of the incoming equipment. Upgrade of any earthing facility, if occurring, is a bonus.
A talk on site is the way to explore possibilities.
 
I don’t think it was, as far as I can remember all the old regs books I’ve got don’t allow the use of pipes carrying flammable fluids.

Well being sad, I have some books dating back to 1900 which say it was acceptable. Would that be 3rd edtion? either way, I've come across quite alot here in yorkshire. some being post war buildings.
 
From my experience .
Old supply. ( rewirable fuse. not cartridge.)
Needs new cut out.
Earth has not been sweated onto incomer. ( probably )
I usually get customer to complain about incomer and supply company usually fit a new one.
You could try scrapping insulation ( sticky bit ) until you see lead.
Then get ya tester on that.
 

Reply to Help! Never seen this before! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
556
loz2754
L

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top