Hi Im currently working for a company wiring heating systems up I have had a Job Pulled up By a QS for the company we contract for
Saying it Failed due to Earth conductor being used as a live and seriously dangerous. Ill explain , I had to run a cable in for The Heating time clock and it was a fair run , I needed Live, Neutral, and 3 switch lives ,making 5. I used 1x 5 core flex as I thought that as the timer control was double insulated then I could Sleeve the earth with Brown sleeving and use it as one of the Switch lives. Am I wrong to do this?
 
Just to add my penny's worth....... I agree with all that has been said before with regards to the regs. however, I also think it is bad practice and the regs. should be clearer and go further and ban this practice.
It was mentioned that as long as the equipment or termination point has been earthed by another means then there is no need for a cable to have an earth and this leaves open the option to use the cpc as a line conductor, however again, it is in the regs. that all circuits must have a cpc for the full length of that circuit regardless of whether it will be used or not, so a bit of a double standard there and now things get a little bit confusing!
I'm feeling a bit lazy today boys, so I'll leave it up to one you fine detectives to find the said reg. I'm talking about, and it is in there.
 
Just to add my penny's worth....... I agree with all that has been said before with regards to the regs. however, I also think it is bad practice and the regs. should be clearer and go further and ban this practice.
It was mentioned that as long as the equipment or termination point has been earthed by another means then there is no need for a cable to have an earth and this leaves open the option to use the cpc as a line conductor, however again, it is in the regs. that all circuits must have a cpc for the full length of that circuit regardless of whether it will be used or not, so a bit of a double standard there and now things get a little bit confusing!
I'm feeling a bit lazy today boys, so I'll leave it up to one you fine detectives to find the said reg. I'm talking about, and it is in there.

Are you referring to reg 412.2.3.2 concerning a CPC at each point in an installation ??

I think you are refering to my post # 10 when I inferred that a CPC may be at that point being their via another conductor.

If you look though at my post #7 I did say that the assessor may have failed it due to the fact that the cable did not have a CPC inside and therefore the cable would not have a protective earth if it was damaged.
 
Last edited:
Cheers malcolm, that's where I read it, and that's all I'm thinking that if the regs. state that a cable must have a cpc for the length of the circuit then guys that are saying they would use the cpc as a line conductor not adhering to this reg. even though the other reg. says it's only the colour G/Y that can't be used for any other purpose than earth. I think I need a lie down and a wee dram!:confused5:
 
I cannot believe anyone would even consider using a conductor intended to be a cpc as a live conductor....even if sleeved at the ends,the dangers are all to obvious. I'm not convinced of your interpretation of 514.4.2.
IMO in order to comply the entire conductor would have to be sleeved over....clearly impossible if the G/Y is contained within a sheath......I disagree with the above, it is not permitted to use a G/Y within a sheathed cable as a live conductor.


I didnt say i agreed with it.

Great thread though chaps!!
 
Hi Im currently working for a company wiring heating systems up I have had a Job Pulled up By a QS for the company we contract for Saying it Failed due to Earth conductor being used as a live and seriously dangerous. Ill explain , I had to run a cable in for The Heating time clock and it was a fair run , I needed Live, Neutral, and 3 switch lives ,making 5. I used 1x 5 core flex as I thought that as the timer control was double insulated then I could Sleeve the earth with Brown sleeving and use it as one of the Switch lives. Am I wrong to do this?
As long as the time clock is class II and the multicore cable's sheathing is at full integrity throughout the run, then the cable will have both fault protection and basic protection and so no cpc will be necessary. The sleeved G&Y conductor will need to be identified at every termination.
 
One problem is if you use the G/Y as a part of the current carrying circuit, you can sleeve it at both ends to indicate this but what if somebody splits the cable somewhere in the middle to run a radial circuit off it?
 
Bad practice, bad design, lazy installation,cheap and nasty..........anybody even thinking of doing this should hang their head in shame, what next?.........allowing the bad and dangerous practice of "borrowed neutrals"?
 

Reply to Help On Using Earth As live? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
196
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top