John J
Trainee
So I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thanks.
2a - Find some lights, print off manufacturers data on said lights
2b - Draw on the positions of the lights
2c - Draw on sockets and FCUs
2d - Draw on each circuit on such a way that a fault with 1 circuit will not affect another
2e - devise a numbering method to ID circuits in relation to the circuit number, room number and/or phase
2f - Draw on any additional distribution boards of you deem th necessary
2g - Draw on lighting circuits in relation to the pool and show switching positions
2h - devise a numbering method to ID circuits in relation to the circuit number, location and/or phase
2i - Annotate drawings with symbols compliant with BS EN 60617.
im the same john stuck on question 2 a 2b right to 2i
Upvote 0
I’m suck with the question attached 615 2365 electrical design project ? question 5 2 hours still can’t work out the answer
Upvote 0
Easy method, use the adiabatic equation to find out the size
S = ✓ I^2 * t / k
I = the current required to operate the device
t = disconnection time required for the device
k = factor given for the cable selected - Typically 115
So for argument's sake, let's say we have a fault current of 320 (taken from your trip curves) a time of 0.1 (taken from your device operating times) and a K factor of 115 (taken from the tables following the trip times)
S = ✓ I^2 * t / k
S = ✓ 320^2 * 0.1 / 115
S = ✓ 102,400 * 0.1 / 115
S = ✓ 10,240 / 115
S = 101.19 / 115
S = 10.05
As there is no conductor with a CSA of 10.5, you select the next size up, in this case 16mm^2
The above is purely and illustration and values may not be accurate but it serves to show how to lay out the equation so that you can understand what is going on at each step.
Hope this helps
Upvote 0
S = ✓ I^2 * t / k
S = ✓ I^2 * t / k
S = ✓ 10,240 / 115
S = 101.19 / 115
S = 10.05
Hope this helps
Thanks for this it’s just different this level 3 as I’m dyslexic not with reading and writing but with maths and new things of of my comfort zone
Upvote 0
What you struggling on? Show us what you have and we'll offer some guidance.
Hi,
I don't currently have any pictures but I've drawn out on the hotel rooms how each would be wired for what the spec asks for. After reading through and breaking down the task sheet and looking around the forum I am beginning to understand this more taking it a bit at at time. I have less than 2 weeks so I was in a bit of a panic.
This is a question I do not understand
"Select, with the aid of manufacturers’ data, a suitable range of circuit protective devices for this
contract. Your selection should be based on the following
 Prospective short circuit currents
 Requirements for additional protection and special locations"
Upvote 0
Hi,
Ok, easy;
Select a suitable range of OCPDs generically (B6, C32 60898/61009s) them download the datasheets from a manufacturer of your choosing and add them to the assignment.
You should be able to calculate PFCs based on Uo and calculated Zs from estimated cable run sizes (assume you have Ze?)
As for special locations, here's a RCD Omission matrix from a different project to help (attached)
Upvote 0
John J
Trainee
Liverpool
HELP PLEASE!!! 2365/615 electrical system designs
Electrician Courses : Electrical Quals
John J,
DPG,
Electrical Courses