Am doing a inspect and test on some work iv done board, re-wired light,
So tncs system ze .16 , PFC 1.5 , all circuit have >500 I.r, R1+R2 readings are what I would expect for run length etc. Problem is my zs on all circuits is coming out .70 more, not the .16 I was expecting!(based on zs=(R1+R2)+ze), Any ideas guys??
 
Why were you expecting 0.16 as Zs ? if youre Ze is 0.16 then the Zs has to be higher without considering any parallel earth paths
 
Sorry I didnt explain that clearly,e.g what I ment was ze.16 + R1+R2 . 20 was expecting zs of .36 there or there abouts what I'm getting is zs of .90????
 
That does seem strange, assuming youare taking Zs at same place as R1 R2 you would expect it as you rightly say to be around the sum of ZE plus R1 +R2 or lower is the norm. Have you got another loop tester to double check

At the end if the Zs is compliant we can be happy but I share your confusion over the difference as it is substantial, lets see if the clever ones can help
 
Woof .. no im a puppy , did you disconnect the main bonds to water gas etc ,and if you did did you do it befor or after you did the Ze ,although when you carry out the R1 R2 test you get a reading you'd expect ,when you do your Zs test the fault current of the circuit now if you have any slightly loose or poor connections the readings could increase to a higher than expected reading for instance doing a Zs on a socket if the terminals are worn when the fault curent is applied it may not make the contact as it should thus increasing the Zs level , i have come across this loads of time on older properties new socket readings improve
 
Are you getting a reading through the rcd main switch (es) or rcbo's when you are measuring the Zs?

This often increases expected results.
 
Hi are the circuits RCD/RCBO protected as you may be measuring the resistance of those when carrying out your Zs test,
Ive encountered this esp. with certain brand RCBO's such as Dorman Smith
Regards, Graeme
 
I'd suspect one of two things..

i) Are you using a loop tester on the 'no trip' setting? If so then this will most likely give in inaccurate reading?
ii)Have a crack at measuring your Ze again, but instead of the supply side, carry the test out on the load side of the MCB/RCD/RCBO's etc. This will enlighten you on wether you are experiencing increased resistance through the devices. Obviously for this, you will need to close the protective devices, so removing the circuit cables first would be a good idea.
 
As IQ says it could be a multitude of reasons , at the end of the day if the R1 R2 readings are satisfactory and the Zs readings are below the max permitted then you have nothing to worry about ,and even less if the installation is fully RCD protected
 
leads are shiney new! tested ze 3 times and zs on all circuits 3 times, no change, tester is however on "no trip" setting, R1+R2 readings are fine and zs reading are fine, just one of those "wonder whats causing that" things!

cheers guys really appreciate it
danny
 

Reply to Help please! Cheers guy!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top