leads are shiney new! tested ze 3 times and zs on all circuits 3 times, no change, tester is however on "no trip" setting, R1+R2 readings are fine and zs reading are fine, just one of those "wonder whats causing that" things!

cheers guys really appreciate it
danny


May I suggest that you test at a location with the high loop reading set (i.e. not on no trip), and then retest at the exact same point on the 'no trip' setting. I did this with my megger to find a it could vary up to 0.5ohms in irregularity..

I created a thread over this subject here
 
vBulletin Message
cagedanimal2010, you do not have permission to access this page. This could be due to one of several reasons:

Your user account may not have sufficient privileges to access this page. Are you trying to edit someone else's post, access administrative features or some other privileged system?
If you are trying to post, the administrator may have disabled your account, or it may be awaiting activation.



its what im getting when trying to access any ideas?
 
oh my apologies, I posted it in the electricians arms forum, didn't realise. I'll copy out of it the basic jargon of the discussion...

I posted....

Hi all,

I've always understood that using the anti-trip setting will normally give an inaccurate reading. However I wasn't so aware of level of it's inaccuracy..
My own tester is a KT64.When I've done a comparison test on it the difference between the non-trip and normal reading many times, and the difference in the reading was only ever up to a maximum of 0.1 ohm.
Today I finally received my Megger from one of my employers, and so I had a play with it today and thought I would check for the difference in readings on this kit.

I measured a Ze of 0.16 ohms, and when I turned it to anti-trip it jumped up to 0.63 ohms. I was somewhat amused that this kit could really apply nearly half an ohm in inaccuracy?? I re-tested a couple of times (allowing a bit of time between tests) and it maintained these readings.

I'm not necessarily concened about this, but I thought I would post on here to see if anyone else has checked out their tester and if the readings are similar to this??

:confused:

to which sintra replied...

Had the same prob with 2 of our megger 1553's. (new at time 2 years ago)
Done the same as yourself and tested a non RCD protected circuit on the high setting and then again on the no trip both meters showed the same inaccuracies of about 0.5 ohms.
Both were sent back to megger and repaired results now are within 0.02 ohms and remain stable as i check them monthly as routine.


then Jason.S said...

I used to have some Megger seperates.

Did exactly the same thing.

Im sure somewhere in the manual it does state this.

then ian added..

I used to have a megger CM500, did exactly the same thing. I spoke to megger and they said it was within there tolerances. I changed to a 1552 and since then everything is fine.

Ian


that's the long and short of it.


:cool:
 
right guys have been playing with my tester and the difference between hi-current and low-current is about .08 ohms, so still not equating to the .70 difference,
so would to rcd main switches cause this? and will the napit assessor pick this up and fail even tho the readings are compliant?
danny
 
Doubt he would fail you, as if that is your measured reading then that is it. He may ask you to show him how you did it, may even ask you why you think there is a difference.

Have you tried doing the test. Cross connect the LINE/CPC at the end of the circuit. Then at your board with obviously the MCB isolated for the circuit, One croc on the load side of the MCB and then the other on the Line inside of the main switch and test.?
 
I think he'll be pleased that you spotted the anomaly and have explanations for it!

Do the test as Malcolm has indicated above (on full current test) and see what reading you get.
 
As IQ has pointed out, if you can explain the possibility for the irregularity, along with your observations they'll be more than satisfied.
 
Have you checked your loop impedance tester with a check box checker to see if it has recently gone on holiday and may need a re-calibration?
 

Reply to Help please! Cheers guy!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top