Hi All,

I hope you guys are well and have had a good day!

its actually my first time on here and I was wondering if you could give me some advice please.

i wired up an oven with a cooker switch and then cooker outlet plate. Did the continuity test and insulation resistance test and everything was ok with results. I then switched the mcb on and everything was fine. I then switched on the cooker switch and the oven went bang!!! The RCD tripped but the MCB did not so looking for an earth fault. Then I disconnected everything. I did an insulation resistance test from the CU to the cooker switch and the readings were greater than 999M ohms. i then did an IR test from cooker switch to the outlet plate. everything was then also ok. i then did an IR test on the cooker lead and the earth to line reading was 0.26M ohms suowing an earth fault. I then connected from the Consumer Unit to the cooker switch and outlet plate without the cooker connected and everything was fine no trips. Could you please help me in deciphering this problem, thank you.
 
PS dont meggar with the hob/cooker connected you may damage it also the low M-ohms maybe the electronics etc in the hob/cooker like timer boards or displays ...hopefully you haven't damaged it with 500v ...another schoolboy error lets hope luck is on yourside.

This is really basic stuff i take it as you state Officer? as occupation you have no hands on experience .... you really could do with gaining some valuable experience under a well weathered competent sparks for a yr or 2 or you'll end up making some costly mistakes.

Dare i ask what kind of course you have done to get qualified and how long it lasted?
 
Last edited by a moderator:
Thanks guys for your help. If I'm honest the large junction box type screws threw me, thus not expecting any markings and nor a link to the metal back. When I've normally connected a cooker it's to the cooker switch direct. Well I shall hope that Lady Luck is on my side and I shall update you tomorrow regarding the cooker. Thank you again for your help.
 
Im not the biggest fan of intensive learning its attractive because its fast but is flawed as you get no onsite real world experience which is a must IMHO to give your theory some real reference...

I would recommend you get an experienced wing man who can guide you for a few years before jumping in he deep end feet first.

You can be taught how to swim through theory in the classroom but the reality could see you struggle if not drown as soon as you take to water.

I hope you take it as constructive advice as the basic mistakes here are worrying even if a moment of stupidity you followed it by Insulation testing with the appliances still connected which is all in your college notes yet you haven't applied it when on site.
 
Thank you. I understand that was not the best thing to do but I immediately just took it as a connection box. I have now rectified that problem. But with the cooker flex into the the hob connection unit now reading at 0.26M ohms, is it safe to assume that the flex will need replacing and the rest of the hob will be ok or is it a case of having to buy a new hob? Your help is greatly appreciated and I still don't know why I did that, it was rather silly of me making that mistake.
leave leccy alone will you...
 
Im not the biggest fan of intensive learning its attractive because its fast but is flawed as you get no onsite real world experience which is a must IMHO to give your theory some real reference...

I would recommend you get an experienced wing man who can guide you for a few years before jumping in he deep end feet first.

You can be taught how to swim through theory in the classroom but the reality could see you struggle if not drown as soon as you take to water.

I hope you take it as constructive advice as the basic mistakes here are worrying even if a moment of stupidity you followed it by Insulation testing with the appliances still connected which is all in your college notes yet you haven't applied it when on site.
i would have thought this young un would have been the wing man Dark...
 

Reply to Help please! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
427
  • Question
I recall where a fluorescent capacitor would cause a separate socket RCD to trip when turning off the light
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top