So if you IR a circuit and you don't get the expected result in my case I expected to get >299 from my Megger instead got 160Mohm why would that be ?



Ty

Why would you expect to get >299Mohm? How old is the actual installation? Over time the IR readings decrease, as long as you have >2Mohm then that is fine. Personally I would look into more if it was down to, say, 5Mohm, but 160Mohm is a good reading.
 
Why would you expect to get >299Mohm? How old is the actual installation? Over time the IR readings decrease, as long as you have >2Mohm then that is fine. Personally I would look into more if it was down to, say, 5Mohm, but 160Mohm is a good reading.

Its 7 years old, on some circuits by doing L-N, N-E, L-E I was getting >299 but on others it would start at 120Mohm then creap up to I 160 and above. Also what about downlighters do you have to remove all transfomers in order to do a proper test or will LN-E suffice


Ty
 
Another question on a new installation were fitting around 60 downlights in one flat and I think they are all going to be transformers..

This would be a pain for our tester to remove all of these but I believe a LN-E test isn't allowed of a EIC??
 
Another question on a new installation were fitting around 60 downlights in one flat and I think they are all going to be transformers..

This would be a pain for our tester to remove all of these but I believe a LN-E test isn't allowed of a EIC??

Correct limitations not permitted on an EIC only on a PIR.

To save disconnecting trannys and removing lamps etc. the best way is to test the circuits before these are fitted and then finish testing when job complete.

We always do testing in at least 2 stages for an EIC.
 
So if you IR a circuit and you don't get the expected result in my case I expected to get >299 from my Megger instead got 160Mohm why would that be ?



Ty


Probably thinking about >299 because when you do these tests on courses you always get >299 but in reality you will often get a reading below and 160 is well above 2ohms so wont need investigating
 
We always do testing in at least 2 stages for an EIC.


Exactly right.

It's called initial verification, then testing and inspection. The requirement for L&N - E when carrying out IR should never occur when doing an initial verification as this testing is done prior to application of loads to the circuits.


Whe carrying out IR on periodics, readings will vary with age due to the degrading of the installation. Although you can justify that 1Mohm is the minimum, you will then assess the other readings and they will affect your decision to the date of the next inspection.
 
Well I thnak you all for your input it has cleared a few things up for me.

I also passed my NICEIC asseesment today, so am over the moon. But I have to say this forum is great if your not sure or need to clarify something.


Cheers to you all



Ty
 

Reply to Help Questions on IR of new consumer unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top