andy100

Hello,

I have a 6mm t&e protected radial circuit running from the CU to the kitchen, this was originally going to feed just a new Neff Oven, rated at 3.68KW total connected load ~ 16Amp. This was fine, but now it turns out that the new Microwave we’re getting is rated at 3.1KW total connected load and the technical specs state it should be protected at 15Amps. The Microwave was originally going to be less powerful and would have been able to connect into a 13Amp FCU off of the mains ring but now I have the problem that I have a single 6mm t&e radial that I need to feed both appliances. I have seen the appendix on the 17th ed and know this is allowed.

I have a 32Amp MCB which will protect the 6mm cable and allow enough current to supply both appliances but I’m concerned about short circuit protection for the appliances themselves as well as protecting the 2.5mm flex tails that will run from the isolator switches to the appliances. Any advice would be much appreciated.

Thanks

Andy
 
Thanks telectrix for the quick response. Do you think I would still need 2 all-pin isolation switches as well or would the main switch within this new enclosure be sufficient for maintaining an all-pin isolation although it would be for both appliances at the same time.
 
thanks engineer54, at the moment, instead of using a dual connection plate, I'm just using a 60amp junction box (as this is big enough to get 3 x 6mm into it)
In = 6mm from CCU
Out = 2 x 6mm to feed each isolator switch then 2.5mm flex to each appliance.

Correct me if i'm wrong, but a dual connection plate still doesn't resolve my issue of short circuit protection for the appliance itself and cable protection (2.5mm flex). Even if I used 4mm flex as i=p/u suggested, the weakest link just moves to the internal wiring of the appliance itself and more importantly the appliance.

thanks for your feedback so far.

Also hob is induction but on a separate circuit.
 
thanks engineer54, at the moment, instead of using a dual connection plate, I'm just using a 60amp junction box (as this is big enough to get 3 x 6mm into it)
In = 6mm from CCU
Out = 2 x 6mm to feed each isolator switch then 2.5mm flex to each appliance.

Correct me if i'm wrong, but a dual connection plate still doesn't resolve my issue of short circuit protection for the appliance itself and cable protection (2.5mm flex). Even if I used 4mm flex as i=p/u suggested, the weakest link just moves to the internal wiring of the appliance itself and more importantly the appliance.

thanks for your feedback so far.

Also hob is induction but on a separate circuit.

Short circuit protection is afforded by the 32A MCB. The appliances are fixed equipment so the flex's/cords cannot overload. So there is absolutely no need to go to the lengths you seem to be going too...


What's more, accessory fuses are there to provide protection for flex/cords, NOT the appliances themselves. If these appliances were portable/moveable then yes you would need a fused plug top or FCU, but not absolutely necessary where fixed appliances are concerned...
 
Last edited by a moderator:

Reply to Help! Supplying two ovens from a single radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
438
  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top