I have a 6mm t&e protected radial circuit running from the CU to the kitchen, this was originally going to feed just a new Neff Oven, rated at 3.68KW total connected load ~ 16Amp. This was fine, but now it turns out that the new Microwave we’re getting is rated at 3.1KW total connected load and the technical specs state it should be protected at 15Amps. The Microwave was originally going to be less powerful and would have been able to connect into a 13Amp FCU off of the mains ring but now I have the problem that I have a single 6mm t&e radial that I need to feed both appliances. I have seen the appendix on the 17th ed and know this is allowed.

I have a 32Amp MCB which will protect the 6mm cable and allow enough current to supply both appliances but I’m concerned about short circuit protection for the appliances themselves as well as protecting the 2.5mm flex tails that will run from the isolator switches to the appliances. Any advice would be much appreciated.

Thanks

Andy
 
Well, for the microwave, it has a 2.5mm 1m flex tail pre-cabled so can't change this anyway.

If the concern is that the 32A MCB is not going to protect the 2.5mm cable then surely you would have another problem with the Oven wiring itself e.g I can see that the onward internal wiring from the connection plate of the oven is at most 2.5mm. So if my 2.5mm cable isn't protected, the oven wiring certainly isn't either. Therefore on that basis I can't see any advantage to change my connection tails to 4mm.
 
So the manufacturers instructions are just being ignored?

Only if they are obviously referring to European type regulations, .....and remember European plug tops and wall accessories do not include fuses!! Yet another reason why chopping a moulded fused plug top from an appliances lead/cord can't and won't void any manufacturer's warranty, no matter what the service company say's, if it is then connected to the mains supply in accordance/compliance with BS7671!!

The big problem with multi national manufacturers instructions, is that rarely do they fully relate to countries outside of the appliances country of origin. Look carefully and you will usually see some form of small print, stating that appliance must be connected to a mains supply in accordance with your countries recognised codes/regulations!!!
 

Reply to Help! Supplying two ovens from a single radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
440
  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top