I have been asked to provide a lighting circuit outdoors for 18 lights on a canopy. The circuit is fed from a toilet block that has a 100A supply to the meter.
The customer has now asked if they can have some extra sockets. They want a 16A commando socket around 60m from the board. They then want to future-proof to allow them to have 2 x 16A commando sockets and a 32A Comanndo socket 130m away from the board. Everything is going underground in a 100mm duct.
I'm trying to work out what size cable to use but I'm struggling to get it so the volt drop is within regs
can anybody help with this, do you think it's possible?
The supply is a single-phase supply. I think I'm still waiting for access to the meter box, but I'm assuming it is at the moment.
if you need any more information please ask
Thanks in advance
The 16A socket 60m away isn't too bad you should be able to get away with 4.0mm² SWA.
Your problems start with the 130m and I would personally put in a submain to another distribution board but you could be looking at a 50.0mm² submain if all sockets are going to be loaded on a 63A supply and you haven't got too much volt drop to worry about between the new board and the sockets.
Reply to help with circuit design in the UK Electrical Forum area at ElectriciansForums.net
Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...