That is exactly what I was thinking, but the table does go down to 0.01 if you can see. Thank you very much for taking the time to look at the calculations.

Is that where I went wrong? Shall I use 0.1 instead of 0.01?

Have you ever come across a situation where you would use 1mm CPC with 6mm cable?

If I changed it to 0.1 I come up with a 2.5mm CPC, which sounds a bit more suitable.
 
It is ok I see my error, I'll try again.

I had to assume a CPC in step 1, I assumed a size of 4mm CPC to get the loop impedance. I based the rest of my calculations on that assumption. Think I'll start again. I have it all wrong I think?
 
Should the time in the adiabatic not be 0.1 instead of 0.01?
Haven't looked at the calculations but if manufacturers' data is available then depending on fault current a definite minimum operating time of 0.01 seconds may be more realistic than the 0.1 seconds in the BS7671 tables. But the calculation will have needed to be carried out with the cable size used to verify otherwise invalid conclusions could be drawn.
 
There was time when 2.5 T&E incorporated a 1.0 cpc, BS6004 reviewed this and upped the minimum to 1.5 due to possible thermal stress which it may suffer under fault conditions particularly with a 30A, BS3036 fuse. Using this basis a 1.0 cpc with a 6.0 line conductor is almost certainly not going to be suitable with your design current.
 
Haven't looked at the calculations but if manufacturers' data is available then depending on fault current a definite minimum operating time of 0.01 seconds may be more realistic than the 0.1 seconds in the BS7671 tables. But the calculation will have needed to be carried out with the cable size used to verify otherwise invalid conclusions could be drawn.

Thank you, so I was right to use 0.01 then :)
 
It is ok I see my error, I'll try again.

I had to assume a CPC in step 1, I assumed a size of 4mm CPC to get the loop impedance. I based the rest of my calculations on that assumption. Think I'll start again. I have it all wrong I think?
Then it tells you that 4mm^2 cpc is adequate as it is bigger than the result of your calculation. It does NOT tell you that 1mm^2 cpc is adequate as your calculations weren't based around that.
 
There was time when 2.5 T&E incorporated a 1.0 cpc, BS6004 reviewed this and upped the minimum to 1.5 due to possible thermal stress which it may suffer under fault conditions particularly with a 30A, BS3036 fuse. Using this basis a 1.0 cpc with a 6.0 line conductor is almost certainly not going to be suitable with your design current.

Thank you, that is what I thought. My calculations are wrong :(
 
Then it tells you that 4mm^2 cpc is adequate as it is bigger than the result of your calculation. It does NOT tell you that 1mm^2 cpc is adequate as your calculations weren't based around that.


I think I get it. So as the result was lower than 4mm2, so now I can go back and try again factoring in a 2.5mm2 CPC, if the result is higher I cant use 2.5mm2 I will have to use 4mm2?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham

Thread Information

Title
Help with CPC size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
Gigsy,
Last reply from
Risteard,
Replies
41
Views
8,184

Advert

Back
Top