Just done a IR test on a light circuit,i test from the C.C.U fluke 1653B,500v, L-E reading 3.17Mohm,is that reading ok?
 
It seems you are confused here. the R1+R2 figure is combined with Ze to give Zs. The insulation resistance readings have their own columns.
The IR of 3.17 Megohms is more than enough to satisfy the current regs.
 
As above....

Zs is calculated from the measured value of Ze + the measured value of R1+R2 at each circuit.

The value of R1+R2 is found when doing continuity of CPC at the extremity of each circuit. The highest value
 
so the value of 3.17Mohms plus the Ze 0.35, should be recorded in column *12, Zs

Dont take this the wrong way,I'm not having a go....but one of the fundamental requirements of testing is a basic understanding of the principles which you clearly dont have. Can I suggest you do some serious schooling before carrying out any more testing?....Or something is going to go horribly wrong and you may end up responsible.....Friendly advise intended,nothing else.
 

Reply to Help with insulation resistance testing on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
283
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top