Just done a IR test on a light circuit,i test from the C.C.U fluke 1653B,500v, L-E reading 3.17Mohm,is that reading ok?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Help with insulation resistance testing on a lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It passes, why don't you think it is ok??
so the value of 3.17Mohms plus the Ze 0.35, should be recorded in column *12, ZsOne bulb is highly unlikely to give you a reading of 3.17 Mohms
so the value of 3.17Mohms plus the Ze 0.35, should be recorded in column *12, Zs
so the value of 3.17Mohms plus the Ze 0.35, should be recorded in column *12, Zs
You've lost me now. Why would you combine the IR reading with the Ze?