Hi Oboe

Firstly step 3 in the ring circuit test is to cross connect the Line and CPC cables not Line and Neutral as you have quoted. I think you may have cross connected Line and neutral and are testing between Line and CPC at the sockets Hence the reason NO readings.

Get a copy of the On Site Guide and look at pages 80-83 The 3 step procedure is detailed with pix

Remember the test is a 2 wire test for continuity so read you're 1552 instruction book for continuity test The leads into the meter are not changed it is the probes that are changed over at each stage

Step one end to end resistances Probe 1 (P1) goes to Line out Probe 2 (P2) goes to line return
Then P1 to neutral out and P2 to Neutral return then P1 to CPC out and P2 to CPC return Record readings

Step 2 Cross connect Line out to neutral return and line return to neutral out
Test between Line and neutral at each socket P1 to line P2 to Neutral Record readings

Step 3 Cross connect Line out to CPC return and Line return to CPC out
Test between Line and CPC at each socket P1 to Line and P2 to CPC operating the switches and testing proves polarity also - Record results

Highest reading at Step 3 is the R1+R2 reading for the test cert

Good Luck and keep practicing Remember OSG page 80
 
Last edited by a moderator:
hello mate, tell me to b%$£*&^s if im telling you to suck eggs, you can use the plug in for radials but ring finals you need the disconnect the live, neutral, earth from either the socket or the board to do your end to end tests & r1+r2 readings to complete the nic sheets. by the time you have disconnected the phase & neutral linked them out then tested you still have to devide the result, because you have two live & two neutral the csa is double the result will be half what it should be you could have stripped the wires out the socket tested & put back together. i usually take the readings from the socket do l, n, e end to ends then cross over l & e so earth from so live from one wire is connected to earth on the other wire & vise versa take the reading & you should get the following or round about - live plus earth devided by 4.
 

Reply to Help with megger 1552 doing ring final circuit test... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
935
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
887
Hi all, I’m in the final stage of my electrical apprenticeship and I need some help to complete my portfolio. I have all units apart from 115...
Replies
0
Views
140

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top