WillWX

-
Joined
Jul 27, 2015
Messages
100
Reaction score
79
Location
Northants
I'm in the process of re wiring a kitchen, the customer has gone with a Smeg Range cooker with a nominal rating of 19.5kw, the circuit is all in, that doesn't worry me.

However the DNO has been out to renew the service head as it was in a poor state, in doing this they have downgraded the cut out to an 80amp/16mm tails.

The max demand is roughly 50amps currently, but I feel once the Range cooker is up and running the max demand is going to be very close to the 80amps.

Would you reccomend to customer to have DNO back to upgrade tails/cut out? I would feel more comfortable knowing there is a 100a/25mm tails incase Mary berry ever pops in to show them how it works..

Any advice is greatly appreciated :)
 
A cooker may have a maximum load of 19.5 kW according to the manufacturer, but if it ever pulled over 30 amps I would be very surprised
 
Diversity applied to cooker as you say is roughly 30 amps.

There are 2 ring circuits, 2 lighting, 16a radial and an immersion heater.

No electric shower, oil heating and no other big loads.

I may we'll be being over cautious here, after doing a walk around and applying diversity based on light points/socket outlets and immersion at 100%.
 
Is this an ordinary domestic kitchen? Who the hell would need a cooker that pulls nearly 85 Amps?? If I were you I would forget about exceeding the maximum load, what cable/OCPD have you put it on? How do you mean the DNO downgraded the tails?
 
Yes, ordinary domestic kitchen, it's ridiculous. I am going to try and explain to them tomorrow morning that in the nicest possible way, it's ridiculous.

I've gone for 10mm/45a or maybe 50a. Ref method C.

The tails from head to meter are now 16mm, I'm sure when I originally looked at the job they were 25mm, however I cannot be 100%.
 
I just looked at their web site and found a 19.5 KW with a listing specifying a 45 amp cooker switch
Even putting any diversity for this to one side and going with it drawing an unlikely 40 ish amp
It leaves you with a constant 40 amp to play with for the rest of the household loads,there appears to be a adequate supply from what appears to be a very ordinary demand
 
Can I ask what was the previous cooker and it's circuit details? But agree that it should not be a problem for them.
 
I just looked at their web site and found a 19.5 KW with a listing specifying a 45 amp cooker switch
Even putting any diversity for this to one side and going with it drawing an unlikely 40 ish amp
It leaves you with a constant 40 amp to play with for the rest of the household loads,there appears to be a adequate supply from what appears to be a very ordinary demand

Thanks, I will leave as is then. :)
 

Reply to Help with Range cooker.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

Complete guess, but it's probably cheaper to let a separate meter read a CT clamp and send the data to the charger's microcontroller using rs485...
    • Like
Replies
6
Views
2K
  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top