R

rick.oshea

Visited a job yesterday in an office to look at extending a ring to add some additional socket points - the existing RCD / isolator which covers the whole installation, is a Wylex 100mA 63A (fitted in the consumer unit). The installation has no 30mA RCD cover on the sockets.

There is a second consumer unit, fed from the output of the 100mA RCD in the first board - this is powering some oil heaters and the timer circuit (through a contactor).

Q. My simplist option was to replace the existing 100mA with a 30mA to bring the installation up to current regulations but wanted to check I'm not missing anything by removing the 100mA RCD and putting in a 30mA in its place - Can't fit an RCBO in the current board (not enough height room in the CU)....just checking I'm not going to introduce a problem, such as nusiance tripping because of the heating circuit / contactor on the second board.

Anyone see any problems?

Any advice would be much appreciated....
 
Last edited by a moderator:
As you've already alluded to, why was the 100mA there in the first place. What type of earthing system is it? TN/TT?

It may be that someone (who didn't know better) just replaced a 30mA with the 100mA because of nuisance tripping.
 
Offices and leakage tend to go one with the other nowadays

Perhaps divert the ring only to a seperate rcd enclosure to the side of the existing board
 
As Des said, I'd be tempted to have the RFC(s) fed from another source. Have you seen the effects on the system (leakage wise) when the timer kicks in and the heaters fire up, that may be the reason for the 100mA at the moment.
 
Have you seen the effects on the system (leakage wise) when the timer kicks in and the heaters fire up, that may be the reason for the 100mA at the moment.

No I haven't (not got a EL Clamp meter :-( will see if I can get my paws on one and take a look next week and then discuss options with Customer ..... that's another one for the ever growing Christmas Tool list!

Thanks for the advice guys
 
For extending a single or a few ring circuits you could take the existing circuit through a 30ma rcd in a surface grp enclosure (usually witin the db cupboard) ideally upgrade the main rcd with a type s rcd for time discrimination. However, whilst you should do this this is no a bs 7671 requirement.
 
Visited a job yesterday in an office to look at extending a ring to add some additional socket points - the existing RCD / isolator which covers the whole installation, is a Wylex 100mA 63A (fitted in the consumer unit). The installation has no 30mA RCD cover on the sockets.

There is a second consumer unit, fed from the output of the 100mA RCD in the first board - this is powering some oil heaters and the timer circuit (through a contactor).

Q. My simplist option was to replace the existing 100mA with a 30mA to bring the installation up to current regulations but wanted to check I'm not missing anything by removing the 100mA RCD and putting in a 30mA in its place - Can't fit an RCBO in the current board (not enough height room in the CU)....just checking I'm not going to introduce a problem, such as nusiance tripping because of the heating circuit / contactor on the second board.

Anyone see any problems?

Any advice would be much appreciated....
How would replacing a 100mA RCD with a 30mA RCD bring the installation up to current standards?
Is there a requirement in the current standards for 30mA RCD protection in this installation?
Is there a location containing a bath or shower, are the socket-outlets used to supply mobile equipment outdoors?
 
I'd assumed 30mA protection would be needed because of the cable runs (ie <50mm in the walls and not mechanically protected).
 
Understand that Malc, I hadn't thought that the whole of the office staff could be deemed skilled in that respect though, if that's the case then fairy nuff :)
 
The requirement for 30mA RCD protection allow excemptions where socket-outlets are to be used by skilled or instructed persons, or where the installation is under the supervision of skilled or instructed persons for both socket-outlets and cables concealled in walls.
It is just for socket-outlets used to supply mobile equipment outdoors, and for circuits of locations containing baths or showers where there are no exceptions.
In order to comply with EARW regulations, anyone using a socket-outlet as part of their work duties, must meet the requirements to be considered skilled or instructed.
It therefore follows that if everyone using the socket-outlets are skilled or instructed, then the installation must be under the control of a skilled or instructed person, perhaps even by many such persons.
 
Don't the sockets also have to be suitable labelled? What happens when the cleaning contractors come around at night etc.
 

Reply to Help with RCD - 100mA to 30mA in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top