evening all,
went to look at a mates cu the other day tt system 30ma rcd main switch tripping out randomly
earth loop to stake 150 ohms.
earth loop with everything connected 1.30 ohms.
before i did any insulation tests i did a full set of rcd tests and it wouldnt trip via my tester (mft1552) however test button did work,

so said i would change cu as replacement main switch for old cu not available,
replaced cu today with wylex dual rcd cu tested circuits as i put them back.

now the odd thing there is one lighting circuit that tests >299 l-n >299 l-e >100 n-e when i connect this it stops the rcd from tripping on test.
swapped rcds round and tried circuit on both side of cu but with this circuit connected rcd will not trip, with it removed it will.

what sort of issue can stop the rcd from tripping

for those who dont know me i am 22yrs time served with 2391



at the mo the circuit is just via mcb not on either rcd
and i am waiting to here if random tripping has stopped

thanks mark
 
at what point on the install did you test the RCDs...at the RCD itself...or further downstream...at a socket perhaps....its just i1`v heard of RCBos that wont test upclose to em...but a bit further downstream...
 
With the L/E/N on the light circuit removed from board did you do a continuity and ohms measurement test from the disconnected ends of the circuit to L/E/N on the board just to double check there isn't a interconnection ?
J
 
Why dont you connect the light circuit switch all the lights off at the switch then test the rcd if this works then move on to switching each individual light on until you get the same problem.
 
I wonder if there are lots of transformers in the circuit,I'm thinking that somehow it is replicating no trip test meter operations, by somehow saturating the circuit with Dc

yes there is some but not a huge number i did try to trip the rcd both loaded and unloaded

could you explain your comment as i dont understand
 
Why dont you connect the light circuit switch all the lights off at the switch then test the rcd if this works then move on to switching each individual light on until you get the same problem.


i did try with all lights on and all lights off still the same but will try again one by one as head was spinning by this point
 
i did try with all lights on and all lights off still the same but will try again one by one as head was
spinning by this point
Me thinks that if you switch each light off on the suspect circuit and the rcd should work then switch one on at a time and if you do track it down to a section that has transformers on it then this needs to be highlighted to the manufacturer and even safety standards as there could be a lot of rcds up the country that will not trip and that aint good.

Plus have you thought about writing to the rcd manufacturer I take it , it was the same make and model you replaced ?
 
Lets deal with this in a logical manner.
So , did you carry out the rcd tests at the CU with all mcbs switched off ?
Did the both rcds test ok with regards to trip times ?
If they did then we know the problem is not the rcds.
 
look....i think its now clear that something on that lighting circuit is causing the RCDs not to let go....so now its been narrowed down to a final circuit...lets start to look at that.....i mean this is standard fault finding practice surely guys...
 

Reply to help with rcd problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
Ok I’ll try this when I’m down
Replies
4
Views
384

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top