evening all,
went to look at a mates cu the other day tt system 30ma rcd main switch tripping out randomly
earth loop to stake 150 ohms.
earth loop with everything connected 1.30 ohms.
before i did any insulation tests i did a full set of rcd tests and it wouldnt trip via my tester (mft1552) however test button did work,

so said i would change cu as replacement main switch for old cu not available,
replaced cu today with wylex dual rcd cu tested circuits as i put them back.

now the odd thing there is one lighting circuit that tests >299 l-n >299 l-e >100 n-e when i connect this it stops the rcd from tripping on test.
swapped rcds round and tried circuit on both side of cu but with this circuit connected rcd will not trip, with it removed it will.

what sort of issue can stop the rcd from tripping

for those who dont know me i am 22yrs time served with 2391



at the mo the circuit is just via mcb not on either rcd
and i am waiting to here if random tripping has stopped

thanks mark
 
I remember going to a job a collegue had been to..... Rcd main switch not tripping so he ordered a new one and i went to fit it on his day off.
When i went to test it, wouldnt trip either so i did my tests and found a low resistance fault between Neutral and earth which turned out to be a trapped neutral in the fused spur. So sorted that and then checked both rcds and both were fine.
Just an idea
 

Reply to help with rcd problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
Ok I’ll try this when I’m down
Replies
4
Views
384

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top