evening all,
went to look at a mates cu the other day tt system 30ma rcd main switch tripping out randomly
earth loop to stake 150 ohms.
earth loop with everything connected 1.30 ohms.
before i did any insulation tests i did a full set of rcd tests and it wouldnt trip via my tester (mft1552) however test button did work,

so said i would change cu as replacement main switch for old cu not available,
replaced cu today with wylex dual rcd cu tested circuits as i put them back.

now the odd thing there is one lighting circuit that tests >299 l-n >299 l-e >100 n-e when i connect this it stops the rcd from tripping on test.
swapped rcds round and tried circuit on both side of cu but with this circuit connected rcd will not trip, with it removed it will.

what sort of issue can stop the rcd from tripping

for those who dont know me i am 22yrs time served with 2391



at the mo the circuit is just via mcb not on either rcd
and i am waiting to here if random tripping has stopped

thanks mark
 
Most gadgets and appliances create "electronic noise" on a circuit which can affect rcd testing - which is why mcbs should be switched off at the time of testing.

My ELECSA assessor, told me to test at a socket or light even on a DB change where you might not be 100% certain of having everyting unplugged or disconnected.
 
My ELECSA assessor, told me to test at a socket or light even on a DB change where you might not be 100% certain of having everyting unplugged or disconnected.

I couldnt give a rats --- what your assessor says lol.
And if all the mcbs are turned off it doesnt matter whats plugged in or not ???

:41:
 
I made the suggestion about equipment perhaps being the problem because,I trust Mark has carried out all the usual tests we would normally do,he has happened upon an unusual problem that requires an unusual cause

I made the reference to the no trip test of a loop tester to give comparison to what I was dreaming about

Dreaming,because I have no technical know how whatsoever, regards the intricacies or the workings of the rcd tester

I did however find this bit of information from a study into the effects

DC in Residual Current Devices
The widespread use of semi-conductor
devices in domestic, commercial and industrial equipment may result in the
flow of non-sinusoidal earth fault currents in the event of equipment insulation
failure. This can occur in certain circumstances where the waveform may be
rectified or chopped and these waveforms are said to contain a pulsating d.c.
component which may desensitise a standard Type AC RCD.

The above is somewhere along the lines of what I was thinking,it may be utter bullcarp and the problem will likely be standard, but its certainly an unusual cause


Some of the equipoment listed includes Phone chargers invertors,transformers etc
 
I made the suggestion about equipment perhaps being the problem because,I trust Mark has carried out all the usual tests we would normally do,he has happened upon an unusual problem that requires an unusual cause

I made the reference to the no trip test of a loop tester to give comparison to what I was dreaming about

Dreaming,because I have no technical know how whatsoever, regards the intricacies or the workings of the rcd tester

I did however find this bit of information from a study into the effects

DC in Residual Current Devices
The widespread use of semi-conductor
devices in domestic, commercial and industrial equipment may result in the
flow of non-sinusoidal earth fault currents in the event of equipment insulation
failure. This can occur in certain circumstances where the waveform may be
rectified or chopped and these waveforms are said to contain a pulsating d.c.
component which may desensitise a standard Type AC RCD.

The above is somewhere along the lines of what I was thinking,it may be utter bullcarp and the problem will likely be standard, but its certainly an unusual cause


Some of the equipoment listed includes Phone chargers invertors,transformers etc
hey no probs Des...i wasn`t having a go mate....it was just a bit of info i picked up some time ago about the old robin D-loc...thats all mate...
 
just to clarify as of now the board has 4 circuits on one rcd and these all test and behave normaly

3 circuits on the other rcd and they also test and behave normally

the problem circuit is just on mcb at mo but would effect either rcd if connected

have just had text to say nothing has tripped since i left at 1pm and on the old board it was going upto 10 times a day

so i am wondering if i have a transformer or something that tested ok cold after cu change but is stopping rcd tripping and also when it gets hot causes insulation fault remember l-e 299 n-e 100
 

Reply to help with rcd problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
Ok I’ll try this when I’m down
Replies
4
Views
384

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top