Location
pembrokeshire, wales
please can someone help me. doing a test on a new build and my results are not matching up. all my Zs are way to high. for example on the cooker circuit measured R1+R2 = 0.04, The measured Ze at the board is 0.08 (PME) so Zs should be around 1.2 but my measured is 0.79 is that right if not any idea's
 
Check the connection of the main earth cable on the MET.

Ps welcome to the forum. And we all know its a typo error and you ment 0.12 and not 1.2 lol.
 
Parallel earths (bonding conductors) may result in a lower measured Zs than a calculated Zs (Ze+(R1+R2)).
Note either, doesn't matter. You can always make a comment on your EIC regarding the spurious looking results if you choose to record the measured Zs results.
 
Good point Gary M but he's getting higher readings not lower readings due to parallel paths.

If all readings are about the same difference on each circuit and not just the cooker, I would be checking terminations on the MET, first place I'd look anyway.
 
thanks for replay all seems ok on the MET. i disconeted and bonds when i got this reading and it went to 0.75 i'm using this job for my niceic inspection on wednesday

So the measured Zs was lower with protective bonding disconnected? 0.75ohms against 0.79ohms?

As a side point - don't disconnect protective bonding on a live installation, especially in front of your NICEIC inspector!

Edit, just seen the typo - should be 0.12ohms and not 1.2ohms for calculated Zs. Id put this down to inaccurate measurement due to the no-trip setting of your meter.
 
the cooker circuit measured R1+R2 = 0.04


​that reading don't lookm right to me. far too low. unless the cable is only about 4m in length.
 
please can someone help me. doing a test on a new build and my results are not matching up. all my Zs are way to high. for example on the cooker circuit measured R1+R2 = 0.04, The measured Ze at the board is 0.08 (PME) so Zs should be around 1.2 but my measured is 0.79 is that right if not any idea's

Your Ze measured value sounds too good to be true!!!
 

Reply to help with Zs. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top